#14318 - 09/19/02 05:32 AM SINGLE CONDUCTOR
EVAD7 Offline
Member
Registered: 03/11/02
Posts: 37
Loc: MN
WHERE DO YOU FIND A CODE REFERENCE TO A SINGLE CONDUCTOR IN A RACEWAY. CAN YOU RUN A NEUTRAL FROM A 240V 3 PH IN A PVC CONDUIT?
Top
Work Gear for Electricians and the Trades
#14319 - 09/19/02 05:55 AM Re: SINGLE CONDUCTOR
George Corron Offline
Member
Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
Single conductors in a raceway are referenced in Chap. 9, Table 1. You will find it is very rarely legal, usually referencing a Grounding Electrode Conductor.

300-3(b) All conductors of a circuit, including the neutral SHALL be contained in the same raceway, trench, etc..

Without a very lengthy explanation, if the neutral is not in close proximity with the phase conductors, your fault levels become unmanageable. They must be very close to each other, unless DC, for the system to function through all it's parameters.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
01/24/17 02:22 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 102 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 10/19/00
Posts: 2724

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals