The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 192 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#143143 - 05/16/05 07:11 PM Low Voltage Transformer Quiery
Brite Spark Offline
Member

Registered: 05/16/05
Posts: 12
Hey everyone, I'm an aussie electrician and i was asked by my apprentice, how many 12V low voltage (50W) downlights can be put on single phase 10Amp circuit breaker. Since i have not encountered this problem in all my years, anyones help would be much appreciated.

Top
Test Equipment:

Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#143144 - 05/17/05 03:29 AM Re: Low Voltage Transformer Quiery
kiwi Offline
Member

Registered: 12/04/04
Posts: 347
Loc: christchurch new zealand
G'day Brite Spark, I thought the watts at the lamps were the same as the watts at the circuit breaker, and the VA rating of the transformers took into account the losses. I suppose the best way of checking is by getting the current clamp out.

Next thing you should do is clip your apprentice round the ear and tell him to stop thinking about his cash-jobs on company time.

Top
#143145 - 05/17/05 04:30 AM Re: Low Voltage Transformer Quiery
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Hi there Brite Spark,
Welcome to ECN, mate.
A standard electronic transformer draws about 250mA from a 230V supply.
And to my reckoning, that's 57.5W a piece.
Now, divide 2300W by that and you get something like 40 transformers.
However, lets be realistic about this, no-one should load a circuit up to that extent.
You still need a certain safety margin.
Generally I wouldn't put any more than 20 on the one circuit.
There was at one time here in NZ, a maximum number of luminaires allowed on the one circuit, but I guess that's all gone now and I don't see that AS/NZS 3000 makes any mention of lighting apart from in a Maximum Demand scenario.
AS/NZS 3018(Domestic Electrical Installations) may have different ideas about that though.
Hope that this helps.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#143146 - 05/18/05 06:09 AM Re: Low Voltage Transformer Quiery
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Just a little point Brite Spark,
Was your apprentice referring to Electronic or the (older,supposedly banned) Wirewound type transformers?.
The wire-wound type draw quite a bit more current, because of the Hysteresis current in the transformer.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#143147 - 05/18/05 10:29 AM Re: Low Voltage Transformer Quiery
djk Offline
Member

Registered: 12/26/02
Posts: 1269
Loc: Ireland
Trumpy,

The rules over here set a maximum of 10 points (lights or sockets) on any one radial. (you can't mix lights and sockets either. 10A for lighting, 20A for sockets)

Obviously, you're supposed to design the radial's load in such a way as to avoid overloading it too, but they're the maximum numbers allowed by the wiring rules.



[This message has been edited by djk (edited 05-18-2005).]

Top
#143148 - 05/18/05 10:59 PM Re: Low Voltage Transformer Quiery
Brite Spark Offline
Member

Registered: 05/16/05
Posts: 12
Hello everyone, i normally load 10A circuit breakers at 2200W. i havent had any problems. 2300w is the max loading on a 10A breaker. Why would you only load the breakers at 50%?

Top
#143149 - 05/19/05 12:07 AM Re: Low Voltage Transformer Quiery
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Just my own opinion Brite Spark, but what would happen if most of the Lighting within an installation was on one or two breakers?.
If one trips, you have quite an area of darkness.
I would like to spread the lighting load over 3-4 Circuit Breakers to make sure that if there was a fault, people would still be left with some light to get to the Switchboard.
It also depends upon what sort of installation you are talking about.
Sure a Minature Circuit Breaker of 10 Amperes will take 25A before it trips under Magnetic trip, but it is the Thermal current you have to be careful of.
Thermal trip will occur at 12.5 Amperes.
Run any circuit-breaker close to that level and you run the risk of Nuisance tripping, due to Thermal effects.
It also depends upon the brand of Circuit-Breaker you are using too.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#143150 - 05/19/05 01:25 AM Re: Low Voltage Transformer Quiery
Brite Spark Offline
Member

Registered: 05/16/05
Posts: 12
Thats true Trumpy, but i've neva had a problem with thermal tripping in domestic situations. Also i put lighting on a separate RCD to Power, just so that if an appliance becomes faulty that there is still lighting to get to the switchboard.

I was at a job last week, they were complaining about the RCD tripping. There was only one RCD for both power and lighting. what do u think is it wise to separate power and light?

Top
#143151 - 05/19/05 02:18 AM Re: Low Voltage Transformer Quiery
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Personally I've always seperated Lighting and Socket-Outlet loads as far as an RCD goes.
AS/NZS 3000 requires that you have at least 2 RCD protected Lighting circuits and at least 2 RCD protected Socket-Outlet circuits.
Considering that most home-owners don't even know that thier house even has RCD's in it,
it seems rather rich that most of the call-outs here are to do with RCD's.
In the worst case scenario, we have had them by-passed here.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#143152 - 05/19/05 11:02 PM Re: Low Voltage Transformer Quiery
Alan Belson Offline
Member

Registered: 03/23/05
Posts: 1801
Loc: Mayenne N. France
You only need one for safety, provided it breaks the whole house supply on detection of a fault. Fitting them to undividual cicuits costs more, but if a power circuit trips you could still have lights I suppose? Can't see the point of more than one on whole house power, except a small advantage in fault location.
Only idiots bypass safety features. Problem is there's a lot of idiots. They're not all locked up yet!
Alan
_________________________
Wood work but can't!

Top