#142450 - 01/15/05 08:54 AM Generator tripping RCDs  
lyledunn  Offline
Member
Joined: Jun 2002
Posts: 159
N.Ireland
A 250Kva three phase 415vgenerator is installed in a small hotel complex and offers an alternative supply to the power company during peak tariff periods.
The generator neutral point is grounded via the power company earth, which is contrary to the requirement that the gen-set should have its own independent electrode with an earth electrode resistance not exceeding 10ohms. The Power Company earth is TN-C-S However, the installation is protected with rcds. These operate arbitrarily on change-over from mains to genny. The change over is automatic and on load but there is a small delay. I thought that perhaps this would lead to voltage transients that may cause nuisance tripping of the rcds. The site electrician grounded the frame of the gen-set to a temporary earth electrode. This seems to have solved the problem. I would appreciate your comments on the possible causes that tripped the rcds.


regards

lyle dunn

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#142451 - 01/15/05 10:59 PM Re: Generator tripping RCDs  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,211
SI,New Zealand
Lyle,
This is an interesting subject actually and I say thanks for the information that you submitted with your post. [Linked Image]
I must say that I'm a little rusty when it comes to Generator Installations.
I'm making a wild assumption in asking if the Generator is a Star (Wye) connected type?.
What I can gather, Lyle, this sounds like a problem with current beng introduced by the Star-point of the Generator, back into the Installation Earthing system.
I could be wildly off the mark here, but I would never fail to drive a seperate Electrode for a Generator, regardless of size.


Let's face it, these days if you're not young, you're old - Red Green grin

#142452 - 01/16/05 05:03 PM Re: Generator tripping RCDs  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Hmmm... Interesting problem. I'm trying to sketch out the arrangement and figure what might have caused it.

I'm assuming that the RCD(s) are located after the transfer switch (i.e. that you don't have separate RCDs on each supply before it).

How was the gen-set frame grounded before? Was it just bonded to the neutral/PME earth? If so, then now that the temporary rod has been added, is that frame-to-neutral bond still in place?


#142453 - 01/17/05 09:27 AM Re: Generator tripping RCDs  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,211
SI,New Zealand
Just a slightly off-topic question Lyle.
How is the Generator connected into the Installation?.


Let's face it, these days if you're not young, you're old - Red Green grin

#142454 - 01/19/05 08:26 PM Re: Generator tripping RCDs  
gideonr  Offline
Member
Joined: Dec 2004
Posts: 161
Edinburgh, Scotland, UK
Was the genny connected in through a double pole contactor? If so then the neutral would have been disconnected too. I think the cause would be static building up on the genny frame, which then runs to earth through the first pole to connect when the contactor goes over. If there are any computers in the system, their power supply filters will provide the earth route.


#142455 - 01/19/05 08:31 PM Re: Generator tripping RCDs  
gideonr  Offline
Member
Joined: Dec 2004
Posts: 161
Edinburgh, Scotland, UK
Ughh! I meant quad pole. Too late at night, must go to bed...


#142456 - 01/20/05 03:30 PM Re: Generator tripping RCDs  
PaulCornwall  Offline
Member
Joined: Jun 2003
Posts: 112
England
Hello strangers.. been movin house and all that..

With regard to the genny problem, as far as i was aware you should have no connection of the earth of the building to the genny earth,, once the genny is running shouldnt you be rely on the genny earth??? Maybe you should convert the building to a TT system??

With regard to the trips triping, maybe you are catching them mid cycle when the genny switches over..??

always a difficult problem gennys, not sure anyone is sure what to do


#142457 - 01/20/05 09:16 PM Re: Generator tripping RCDs  
uksparky  Offline
Member
Joined: Jul 2004
Posts: 200
UK
Uhuh LD; come across this little number before. Finished up with splinters from scratching my head too much!

The gen-set must be earthed, and so too an independent earth provided for the installation. Any earth between the genny and the installation can be removed if you get nuisance-tripping provided that the main earth terminal is securely grounded. I have even seen the PME link removed in standby mode - but this shouldn't be required.

The RCD will be downstream of the change-over switch, and nuisance-tripping will also occur from on-load switching transients causing an imbalance in the active-neutral, combined with parallel paths through earthing arrangements. The intermittent nature may be due to this only occuring when certain loads are 'online' at the time the change-over occurs.

If the genset and installation are electrically seperate ( from the earthing point of view ) you should have no problem as the ECL exists only 'within' the installation 'circle'.


If hindsight were foresight, we'd all be millionaires!

#142458 - 01/21/05 02:56 PM Re: Generator tripping RCDs  
lyledunn  Offline
Member
Joined: Jun 2002
Posts: 159
N.Ireland
Sorry guys, been away on a course. It was good of you all to respond.
Ok, between myself and the site spark we have established that take the genny spike out, rcds trip - not always but often. Put the spike back (and its actually just pushed into soft earth adjacent the generator housing)problem resolved. RCDs ARE ELECTRONIC and are of course,placed downstream of the 4-pole change-over switch. Trumpy, Paul; genny is star connected. Neutral connected to frame and thence to installation earth. Paul Cornwall; I cant see how the two earths would be separated lest a link was fitted. I think this arrangement is only used where harmonics are of a concern on parallel sets. UK Sparky, I need to think about what you are saying before further comment.
I do appreciate all your comments.


regards

lyle dunn

#142459 - 01/21/05 03:39 PM Re: Generator tripping RCDs  
lyledunn  Offline
Member
Joined: Jun 2002
Posts: 159
N.Ireland
Uk sparky, just as a foot note. I am having a little difficulty thinking about removing the link from the met to the genny. This would require a new electrode at the installation met thereby converting system to TT. The system currently is TN-C-S on poco supply and TN-S on genny. The genny earth is to reference neutral with earth to stop the genny neutral floating. Fortuitous contact with earth via the met is certain as this is a steel frame building. The genny earth could really be described as superfluous in this case. However, I do recognise the point that when the gen-set is independently spiked there seems to be a cure to rcd tripping so obviously something is afoot! I have drawn the circuit arrangements out and I can see no advantage in separating the gen-set earth from the met.
The reason that I highlighted the fact that these rcds are electronic with loss of neutral protection is that it has been well reported that upstream faults can upset them.


regards

lyle dunn

Page 1 of 2 1 2

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,137
Joined: May 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.8182 MB (Peak: 0.9957 MB) Zlib enabled. Server Time: 2017-03-29 07:17:30 UTC