The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm² flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 175 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#141217 - 06/27/04 07:54 AM Comparing ampacities
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
Hello!

I was inspired to adapt the NEC table 310.16 to metric wire sizes by a thread at MH. Said and done, I've put the result on a webpage.

DISCLAIMER: DON'T USE THESE VALUES!
www.global-electron.com/Ampacities_NEC.htm

I added a 70C column too. I was I bit surprised at the results.

Top
Test Equipment:

Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#141218 - 06/29/04 02:50 AM Re: Comparing ampacities
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
How did you derive the figures for the standard European size cables (1.5, 2.5, 4. 6 mm etc.) in this table?

Here are the U.K. IEE ratings for Romex-style cables: http://www.tlc-direct.co.uk/Figures/Tab4.7.htm

Top
#141219 - 06/29/04 06:30 AM Re: Comparing ampacities
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
Oh, I just made them up...

No, seriously, what I did was to fit a curve to the existing data. As I have the AWG sizes in mm² it is easy to add the in between metric sizes along the curve. Then I rounded the ampacities to the nearest lower 5 Amperes. (The original table appears to have been rounded to the nearest lower or higher 5 Amperes.)

Top
#141220 - 06/29/04 03:07 PM Re: Comparing ampacities
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Ah.... I wasn't sure if you had interpolated the values from the trend of the NEC values, or whether maybe you'd pulled them from Swedish wiring rules.

Top
#141221 - 06/30/04 10:30 AM Re: Comparing ampacities
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
I've fixed the correction factors and extended the column up to 80C. (I got a few values slightly wrong the first time.)

The correction factors turn out to be the same on both sides of the pond. I found the factors had been calculated using this simple formula:

factor = root( (Temperature rating of conductor - actual ambient temperature) / (Temperature rating of conductor - reference ambient temperature) )

If you have a table with ampacities at 30C but the actual ambient is 40C and the conductor is good for 60C you calculate it as:

root((60-40)/(60-30)) = 0.82

Top
#141222 - 06/30/04 11:06 AM Re: Comparing ampacities
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
The above formula allowed me to make a better calculation of the 70C column. This raised the ampacity for some gauges slightly.

Top
#141223 - 07/02/04 02:06 AM Re: Comparing ampacities
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
C-H,
Just a small question.
What type of cables are we talking here?
And what type of installation method?.
Clipped direct w/ ventilation or in Conduit?.
Usual plain cables here have a maximum temperature rating of 75C, when clipped to timber in a roof and that is without the load current that they may be carrying.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#141224 - 07/10/04 06:28 AM Re: Comparing ampacities
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
I think I've got the tables into a legible form now.

Mike,

the NEC gives the names of a whole number of cables. For the time being, I haven't included them, but it appears to include all cable commonly used in the US.

Maybe some of the Americans would like to shed some light on when you can and cannot use table 310.16?

P.S. I'll try to go the other way as well and add AWG sizes to the Swedish or British tables. (It is bigger, as there are tables for clipped directly/free air, in thermal insulation and so on. Not to mention correction factors...

Edit:

I played a little more with Excel. It turns out that the ampacities of Table 310.16 match those in the column "One two core cable enclosed in conduit on a wall or in trunking" (*) in the IEE regs.

* I got the data from a cable manufacturer. The column is probably called something else in the actual regs.

[This message has been edited by C-H (edited 07-10-2004).]