The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 9
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 203 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#140827 - 05/12/04 11:55 AM Generators
PaulCornwall Offline
Member

Registered: 06/02/03
Posts: 112
Loc: England
Hello fellow sparks.. long time no type..

work has gone crazy and i cant keep up..
i have a small problem if any one can help..

A small factory is installing a generator to supply there 3 phase machinery as the supply company want millions to put in 3 phase..when the genny is running it will power the lights and sockets as well via a change over switch,, my problem is the earthing,, i would myself stake the genny and bond to the earth of the building, your thoughts please.

Paul

PS .. anyone know the calculation to convert Kva to Amps

[This message has been edited by PaulCornwall (edited 05-12-2004).]

Top
Test Equipment:

Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#140828 - 05/12/04 01:00 PM Re: Generators
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Three phase system
kVA/volts/1.73=amps
_________________________
Ron

Top
#140829 - 05/12/04 02:50 PM Re: Generators
PaulCornwall Offline
Member

Registered: 06/02/03
Posts: 112
Loc: England
Thanks for that Ron,,, would i be right in saying that a 140kva genny would be 100 amps.. {per phase of course}

Top
#140830 - 05/13/04 04:33 PM Re: Generators
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
140kVa / 415V / 1.73 = 195 amps.

The genset certainly needs its frame bonding to the building's earthing system. You also need to make sure that the genny's neutral is earthed, but in such a way as not to create parallel neutral paths via the earthing system.

Top
#140831 - 05/16/04 06:14 AM Re: Generators
FWL_Engineer Offline
Member

Registered: 05/15/04
Posts: 53
Loc: Barnet, Hertfordshire, UK
I have installed many Gen sets over the years, and they should all be bonded to the Building Earth, however it is also a good idea to stake them as well.

I agree with Paul, you need to ensure that the Neutral is not parallel grounded or there could be serious consequences.

If they are going to run their 3 phase kit from a Gen set, would it not be a wise idea to run the entire installation from it..then use the single phase mains as an emergency backup for essential services in the event of Gen set failure?
_________________________
Click me if you dare \:\)

Top
#140832 - 05/18/04 03:39 PM Re: Generators
lyledunn Offline
Member

Registered: 06/30/02
Posts: 159
Loc: N.Ireland
Paul,
Genny earth reference electrode is not an option, it is a must! Regulations require it to be independent of po-co supply earth, just in case that earth is lost.
_________________________
regards

lyle dunn

Top
#140833 - 05/22/04 11:35 PM Re: Generators
PaulCornwall Offline
Member

Registered: 06/02/03
Posts: 112
Loc: England
Thanks for your replies..
i have been on holiday..

Thanks Paul for the calculation advise..forgot to call 140kva ..140,000..that would give me approx 65 amps per phase??

In reply to all your replies.. the building has a mains single phase supply, i will be installing a 3 phase dis board,, fed off this via a change over switch will be the buildings existing single phase supply, so when the genny is running it will have to power everything, machines and building,, when the genny is stopped he can then put the lights and power back on to the mains,, he would not obviously be able to have both on at the same time..

With regard to the neutral, i would assume a 4 core cable (3 phase and neutral) would run to the genny where the neutral would be bonded to to the gennys earth..
i cant see that any parrallel paths would be created if it was connected in this way..

i said i have just come back from my hols in Portugal.. if any one is interested the colours in domestic houses are black,,phase.. blue neutral.. ??? will they be changing too??

many thanks guys..

Top
#140834 - 05/23/04 12:16 PM Re: Generators
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Welcome back to Blighty! Looks like you brought some summer back with you.....

 Quote:
forgot to call 140kva ..140,000..that would give me approx 65 amps per phase??

Nope. 140kVa / 415V / 1.73 = 195A per phase, assuming an evenly balanced load.

 Quote:
With regard to the neutral, i would assume a 4 core cable (3 phase and neutral) would run to the genny where the neutral would be bonded to to the gennys earth..
i cant see that any parrallel paths would be created if it was connected in this way..


What is the earthing system on the existing single-phase supply? TT? TN-C-S?

Top
#140835 - 05/23/04 02:25 PM Re: Generators
PaulCornwall Offline
Member

Registered: 06/02/03
Posts: 112
Loc: England
Hello Paul

Ok i am havin a blonde day here, got it now.. yes i am a spark

I will have to presume the earth is a TT,, it is very rural.. if you want i can check it out later in the week..

[This message has been edited by pauluk (edited 05-25-2004).]

Top
#140836 - 05/23/04 02:34 PM Re: Generators
PaulCornwall Offline
Member

Registered: 06/02/03
Posts: 112
Loc: England
look i cant even get the smilies to work.................... :rolleye