#139956 - 01/06/04 03:39 PM Voltage at earth electrode
lyledunn Offline
Member
Registered: 06/30/02
Posts: 159
Loc: N.Ireland
On attempting to measure the earth electrode resistance on a single-phase TT installation using an AVO earth loop impedance tester, the instrument indicated over limit voltage of 290v and would not permit the test to proceed.
The P-N voltage was 235v. Unfortunately the operative did not measure neutral to earth voltage.
A contractor on site at the same time as our operative confirmed the 290v using a different voltage indicator.
I was intrigued and some days later I visited the site. Voltages seem to have returned to normal, 233v between live conductors and between phase and earth and 0 v between neutral and earth.
The supply to the installation is fed via a local three phase power company tx.

Care to speculate?
_________________________
regards

lyle dunn
Top
Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
#139957 - 01/07/04 02:06 AM Re: Voltage at earth electrode
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
Maybe a bad neutral somewhere on the network?
Top
#139958 - 01/07/04 10:30 PM Re: Voltage at earth electrode
chi spark Offline
Member
Registered: 01/06/04
Posts: 105
Loc: Chicago IL USA
Imbalance on delta tx?
Top
#139959 - 01/09/04 01:13 AM Re: Voltage at earth electrode
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
lyle,
Would you care to give the type of Line-Earth loop tester used? (ie: Model No.)
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#139960 - 01/09/04 02:35 AM Re: Voltage at earth electrode
lyledunn Offline
Member
Registered: 06/30/02
Posts: 159
Loc: N.Ireland
Trumpy,
Sorry Trumpy, misinformation! The instrument was actually a Robin loop tester. It appears that the indicated voltage can be out by 10% although this wouldnt have necessarily been the problem.
The installation was not connected to the supply at the time. The NIE engineer suggested capacitance which disappeared when the installation was connected. Not sure about that one!
Many thanks for your replies guys!
_________________________
regards

lyle dunn
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals