The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
Yesterday at 09:52 PM
Safety at heights?
by gfretwell
Yesterday at 07:16 PM
failed home inspection.
by gfretwell
Yesterday at 07:03 PM
Webmaster > Admin
by Admin
Yesterday at 05:49 PM
Old Bath Fan
by gfretwell
Yesterday at 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
0 registered (), 0 Guests and 175 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#139213 - 10/24/03 12:22 PM Fault voltage detector
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2349
Loc: Vienna, Austria
I found a cool piece of old equipment. It's a fault voltage circuit interruptor intended to detect ground faults. It's got 2 ground connections, 1 for the incoming ground (auxiliary ground) and 1 for the load ground. If there was a voltage between load ground and auxiliary ground exceeding 50V it tripped. It's a 10x10x10cm box, still wired to a long piece of old NYM cable with the colors black, black, blue, grey and red. Auxiliary ground seems to be a long green wire.

Top
Test Equipment:

Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#139214 - 10/24/03 12:31 PM Re: Fault voltage detector
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
That sounds like the old British voltage-operated ELCB (Earth-Leakage Circuit Breaker), commonly used as the ground fault protection in rural areas in the past ( U.K. Power Systems , diagram #4).

There are still plenty of these in service in this area.

Top
#139215 - 10/25/03 02:05 AM Re: Fault voltage detector
Trumpy Offline


Member

Registered: 07/05/02
Posts: 8553
Loc: SI,New Zealand
Ragner,
These units are still in use over here too.
But our units have an arbitary value of trip @ 25VAC.
Only used in areas, where the basics of the MEN supply can't be met, with respect to Fault currents (Earth resistance/Neutral Return).

[This message has been edited by Trumpy (edited 10-25-2003).]
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#139216 - 10/26/03 07:27 AM Re: Fault voltage detector
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
These devices used to be the norm across large area of rural England, before PME was extended and before the current-operated ELCB became common-place.

They were required to trip at 50V maximum, but many actually trip well below that threshold. I've seen a few that will trip out on under 10V.