#139213 - 10/24/03 12:22 PM Fault voltage detector
Texas_Ranger Offline
Member
Registered: 12/17/01
Posts: 2391
Loc: Vienna, Austria
I found a cool piece of old equipment. It's a fault voltage circuit interruptor intended to detect ground faults. It's got 2 ground connections, 1 for the incoming ground (auxiliary ground) and 1 for the load ground. If there was a voltage between load ground and auxiliary ground exceeding 50V it tripped. It's a 10x10x10cm box, still wired to a long piece of old NYM cable with the colors black, black, blue, grey and red. Auxiliary ground seems to be a long green wire.
Top
Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
#139214 - 10/24/03 12:31 PM Re: Fault voltage detector
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
That sounds like the old British voltage-operated ELCB (Earth-Leakage Circuit Breaker), commonly used as the ground fault protection in rural areas in the past ( U.K. Power Systems , diagram #4).

There are still plenty of these in service in this area.
Top
#139215 - 10/25/03 02:05 AM Re: Fault voltage detector
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Ragner,
These units are still in use over here too.
But our units have an arbitary value of trip @ 25VAC.
Only used in areas, where the basics of the MEN supply can't be met, with respect to Fault currents (Earth resistance/Neutral Return).

[This message has been edited by Trumpy (edited 10-25-2003).]
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#139216 - 10/26/03 07:27 AM Re: Fault voltage detector
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
These devices used to be the norm across large area of rural England, before PME was extended and before the current-operated ELCB became common-place.

They were required to trip at 50V maximum, but many actually trip well below that threshold. I've seen a few that will trip out on under 10V.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 37 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals