The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 9
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 203 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#138761 - 09/26/03 12:43 PM Renley HV drop-out fuses
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Received this request by e-mail. It's a little out of my line, so maybe some of our HV linemen have some suggestions:

 Quote:
Hope you can help. We are working on a project in Azerbaijan and we urgently need to source a supply of fuse wire (3A) for Renley drop out fuses. Voltage is 11kV and 6kV. Urgently required.

Thanks

K.C. Lax
Corroconsult Group of Companies
UK Tel +44 1952 740234 Fax +44 1952 740412
Web site www.corroconsult.com


I've pointed Mr. Lax to this thread, but I don't doubt a direct e-mail would be appreciated if you can help: ken.lax@corroconsult.com.

Thanks guys!

Top
Test Equipment:

Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#138762 - 09/26/03 08:54 PM Re: Renley HV drop-out fuses
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Paul,
I have just sent Mr Lax an email regarding this dilemma.
Normally you can use tinned copper wire of 0.15mm CSA for a 3A DO fuse.
Having said that, all our new drop-out fuses come as an HRC link and are factory sealed.
BTW, Renley is an Irish company and their website is at http://www.iol.ie/~renley .
BTW, Paul, thanks for the referral, it's great to be able to help!.

[This message has been edited by Trumpy (edited 09-27-2003).]
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#138763 - 09/27/03 08:27 PM Re: Renley HV drop-out fuses
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Just on the subject of HV drop-outs,
we tend to only use NZ made units over here, this could be put down to small country protectionism, but we've had the odd problem with these fuses welding into the holders.
We tried using a Swedish brand and we've had no problems at all with them, can't remember what brand they were though, they seemed to have a higher quality of manufacture.