The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by HotLine1
52 minutes 53 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#13787 - 09/11/02 06:07 PM G.E. TQL Breakers
derater Offline
Member

Registered: 03/30/02
Posts: 182
Anyone know who has these in duplex s.p.
They have large cross slots at buss end.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#13788 - 09/11/02 06:45 PM Re: G.E. TQL Breakers
Electric Eagle Offline
Member

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
Clarification - When you say duplex do you mean a breaker with 2 double pole breakers in one or are you talking about tandem breakers?

Anyway, to the best of my knowlege GE does not make a duplex or tandem breaker, instead most of their panels accept half space breakers (THQP series) which can be connect together to make double pole breakers. They do have THQP double pole breakers. I may be wrong or not even answering your question, but that's the best of my knowlege, hope it helps.

[This message has been edited by Electric Eagle (edited 09-11-2002).]

Top
#13789 - 09/11/02 10:03 PM Re: G.E. TQL Breakers
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
GE THQL Breakers and panels are protected from installing too many breakers by design of the half-size "non-CTL" breakers to only be compatible with, say, 20 space panels. Older design GE's aren't compatible at all.

The bus attachment point looks like this: -|-
rather than the single: |

Check the listing on this, but Cutler Hammer and Sq D Homeline make tandems that will fit into a GE bus.
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#13790 - 09/12/02 03:37 AM Re: G.E. TQL Breakers
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
i think T&B makes one to fit 8 panels.....but the 'listings' may be conflicting......

Top
#13791 - 09/12/02 04:08 AM Re: G.E. TQL Breakers
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
I have seen the GE 1/2 size breakers and also full size tandems. Wherever you live find a supplier that sells GE products or check Home Depot.

Top
#13792 - 09/12/02 06:10 PM Re: G.E. TQL Breakers
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6805
Loc: Brick, NJ USA
If I knew how to create a link, I would; but alas:

Search engine: GE Supply; Power & Distribution

They have a listing of local branches, and an online catalog.