The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (LongRunner), 232 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#13719 - 09/10/02 03:56 AM 1 1/2" or 2" PVC LB
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I have to "sleeve" 100 amp al. SER (3 #2, 1 #4) for physical protection. (TODAY!) I will need to run it through a PVC LB.
I would like to keep the piping as small as possible, but I'm afraid a 1 1/2" LB will be too tight.
Any (quick) help out there?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#13720 - 09/10/02 04:05 AM Re: 1 1/2" or 2" PVC LB
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
If 2" isn't too big for any reason other than asthetics, I've often found that 2" is cheaper than 1-1/2", simply because they sell so much more of it.

Getting SER through an LB a few too many times has convinced me that it's cheaper to pipe all the way and use PVC and RHW-2, plus the installation lasts much longer.
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#13721 - 09/10/02 04:10 AM Re: 1 1/2" or 2" PVC LB
tsolanto Offline
Member

Registered: 09/03/02
Posts: 131
Loc: Long Island NY
You can use a 2" LB with 1 1/2 PVC just buy a reducer. The amount of time and effort you will save over struggling to get the SER into the 1 1/2 LB will be worth it.

Top
#13722 - 09/10/02 05:19 AM Re: 1 1/2" or 2" PVC LB
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Duuuh!
A reducer! I can't believe I didn't think about it.

Thanks, guys

Top
#13723 - 09/10/02 07:46 AM Re: 1 1/2" or 2" PVC LB
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
I know its common practice to use larger LB with reducers and have done that many times myself, but how are you going to support the LB? The conduit is only permitted to support conduit bodies of the same trade size as the conduit. See 352.10(H) for rigid nonmetallic conduit and Exception #1 to 314.23(E) for rigid, IMC and EMT.
Don
_________________________
Don(resqcapt19)

Top
#13724 - 09/10/02 08:53 AM Re: 1 1/2" or 2" PVC LB
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
What I'm doing is running an SER feeder through the basement and crawl space of a 1st floor unit, out the wall and up into the second floor to feed the panel.
I am using the PVC (about 12' with an LB at each wall penetration) for some physical protection.

Ah well, 2" it is.

[This message has been edited by Redsy (edited 09-10-2002).]

Top
#13725 - 09/11/02 04:53 AM Re: 1 1/2" or 2" PVC LB
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Job done.
2" -- fairly easy.
1 1/2" would have been a mistake.

Top
#13726 - 09/11/02 02:40 PM Re: 1 1/2" or 2" PVC LB
tsolanto Offline
Member

Registered: 09/03/02
Posts: 131
Loc: Long Island NY
I usually run a screw through the back of the LB into the wood sheething of the house. Not sure if its legal but it works well especially when I am trying to get the SER or SEU into the house. It adds a lot of stability to the LB.

Top
#13727 - 09/11/02 05:43 PM Re: 1 1/2" or 2" PVC LB
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
tsolanto,

Using a screw in the back of the LB. I was doing that for many years. It works well, and I am not sure if it is against the code. I wouldn't fail that job if I was inspecting. After all the pipe is there just to protect the wire from damage.

Top
#13728 - 09/12/02 10:31 AM Re: 1 1/2" or 2" PVC LB
WARREN1 Offline
Member

Registered: 05/09/01
Posts: 184
Loc: Greenville, SC, USA
Art. 370-23 of the 1999 Code does not address the use of screws. Art. 370-23(b)(1) addresses the use of nails, and "they shall pass through the interior within 1/4 inch of the back or the ends of the enclosure." However, I would prefer screws as they would not pull out as easily as nails. IF one considers the LB as an enclosure, then par. (e) would not allow screws or nails, but requires support within 3 feet of the enclosure. I must assume the Code means a strap support, and that would be my preference. In any case, the local AHJ has the final say.