The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 184 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#137080 - 05/25/03 03:56 PM Lightning conducyors
lyledunn Offline
Member

Registered: 06/30/02
Posts: 159
Loc: N.Ireland
There is a requirement in the UK to bond the lighning conductor to the electrical installations main earth terminal. I cannot see any advantage in this, any comments?
_________________________
regards

lyle dunn

Top
Test Equipment:

Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#137081 - 05/26/03 11:24 AM Re: Lightning conducyors
j a harrison Offline
Member

Registered: 05/22/02
Posts: 112
Loc: southampton, england
Lyledunn,

In regard to your enquiry, i have never had to bond a lightning conductor to the main earthing terminal of any installations here in England,

I will look up the relevant codes in regard to this but i am sure we dont have to,
most of the specialist companies take a lighting conductor staight to the ground, i cannot see any point in linking it to the main earth conductor.
John H

Top
#137082 - 05/26/03 11:35 AM Re: Lightning conducyors
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Most bonding requirements are to make sure that a mimimum of potential difference can exist between exposed metalwork in the event of a fault (or in this case, a lightning strike).

I have to admit that I'd need to check this point myself, as I've never yet worked on any building with a lightning rod.

Certainly when installing radio masts and such like, I would always securely ground and bond the mast.

Top
#137083 - 05/26/03 12:40 PM Re: Lightning conducyors
David UK Offline
Member

Registered: 10/03/02
Posts: 134
Loc: Inverness, Scotland
Yes you do have to bond lightning protective system, see Reg. 413-02-02 (vi) in BS 7671: 2001.

Top
#137084 - 05/27/03 11:21 AM Re: Lightning conducyors
james S Offline
Member

Registered: 05/13/03
Posts: 102
Loc: West England
I have not came across this myself, but have recently observed a new bank of mobile phone masts being installed in the grounds of my work place and noticed they ran there lightining conductor (which was i noticed, insulated?) straight onto there own earth rod!


Is it a good idea to introduce such high voltages towards an earthing system which is not struck?

Top
#137085 - 05/27/03 12:10 PM Re: Lightning conducyors
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
 Quote:

I have not came across this myself, but have recently observed a new bank of mobile phone masts being installed in the grounds of my work place and noticed they ran there lightining conductor (which was i noticed, insulated?) straight onto there own earth rod!


I think I've seen this too. Alongside the electrical panels on this floor, there are bundles of cables going up to the roof where there are a lot of antennas. Among the wires is a thick green/yellow wire, which I assume is a lightning conductor.

 Quote:

Is it a good idea to introduce such high voltages towards an earthing system which is not struck?


Despite the fact that ordinary lightning conductors are bare and run close to buildings, they protect the building. I guess the insulation can be there simply to keep people from touching the wire, i.e. not introducing a shock hazard beacause of different potentials.

OTOH, the insulation on the wire can withstand a higher voltage than normal for the very short period a lightning lasts and if the lightning has a good path to earth, it is not going to jump to find another path.

(Personally, I still don't like it. I think the conductor it has to withstand hundreds of kilovolts, something which requires several millimetres of insulation. But then, I'm just a student who doesn't know this field.)

[This message has been edited by C-H (edited 05-27-2003).]

Top
#137086 - 05/27/03 03:45 PM Re: Lightning conducyors
lyledunn Offline
Member

Registered: 06/30/02
Posts: 159
Loc: N.Ireland
Thanks to all.
Paul, I fully realise the purpose of equipotential bonding conductors as minimising fault voltages between exposed and extraneous conductive parts within the so-called equipotential zone. However, I am not convinced that there is any valuable purpose served in this respect by connecting to the lightning conductor. Equally, on loss of neutral on a TNCS system it would actually be better if the lighning conductor was separated from the MET. In fact imagine that all BS7671 requirements were met and that some guy was about to test the down conductor. So he separates the down conductor from the earth electrode. At that moment a fault occurs in some circuit in the installation which will raise the potential at the MET with respect to earth.The same voltage will appear at the disconnected down conductor with respect to earth. A rareity perhaps but nonetheless a distinct danger!
_________________________
regards

lyle dunn

Top
#137087 - 05/30/03 07:32 PM Re: Lightning conducyors
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Lyle,
I would not personally use the mains earth as a Lightning conductor Earthing point.
I would instead drive a seperate electrode for this.
The reason for this being, while lightning has a reasonably high voltage, it has an even higher current (500kA) and introducing this level of current into an Electrical system, no matter how good the Earthing connections are, is not really my idea of a good time.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top