The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 186 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#136650 - 04/20/03 11:04 AM Derating needed?
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
I found this photo on a website promoting an electrical engineering company. Do you think this installation of theirs needs derating?


Top
Test Equipment:

Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#136651 - 04/20/03 06:02 PM Re: Derating needed?
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
C-H,
They're Data cables aren't they?.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#136652 - 04/21/03 08:02 AM Re: Derating needed?
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
Eh, could be. Didn't think of that...

Top
#136653 - 04/21/03 11:07 PM Re: Derating needed?
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
C-H,
Sorry to pour cold water on your idea, mate.
But the question does beg asking, even if those cables are carrying relatively low currents, do they heat up to some extent?.
Given that they are so tightly bundled and all cables exhibit electrical resistance along thier length.
And it looks like those particular cables are running for a fair stretch!.
There's nothing like a neatly bundled and tied cable installation, though.

[This message has been edited by Trumpy (edited 04-22-2003).]
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#136654 - 04/22/03 11:27 AM Re: Derating needed?
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
Well, either my idea or the wiring needed cold water poured on it.

[This message has been edited by C-H (edited 04-22-2003).]

Top
#136655 - 04/22/03 12:19 PM Re: Derating needed?
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
That definitely looks like bundled data/TelCo cables.

As for heat dissipation, if we take a typical telephone cable the conductors might have a resistance somewhere in the region of 28 ohms per 1000 ft.

At a loop current of 100mA (which is toward the high side anyway), I^2*R comes to 0.28W over 1000 ft., or 0.56W allowing for the both sides of the loop.

That's 560 microwatts per foot for each operating circuit. Put away the fork -- You're not going to toast marshmallows on those cables!