The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 238 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#136050 - 03/08/03 03:22 AM Ground ring
lyledunn Offline
Member

Registered: 06/30/02
Posts: 159
Loc: N.Ireland
I note that in US ground rings are employed in buildings. Is it common practice for the Power Co not to provide an earth facility?
_________________________
regards

lyle dunn

Top
Test Equipment:

Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#136051 - 03/08/03 03:42 AM Re: Ground ring
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Lyle,

The PoCo doesn't supply a separate earth connection as in TN-S.

All services in the U.S. are arranged as what would be called TN-C-S or PME over here. The building's earth system is always bonded securely to the supply neutral, along with bonds to ground rods (or rings), water, gas, etc. In fact, at the main distribution panel the neutral busbar is bonded directly to the metal casing (isolated at sub-panels).

The NEC actually prohibits the use of TT systems which are common in Britain & Europe:

 Quote:
250.4 General Requirements for Grounding and Bonding.
(A) Grounded Systems
(5) Effective Ground-Fault Current Path.
..... The earth shall not be used as the sole equipment grounding conductor or effective ground-fault current path.



[This message has been edited by pauluk (edited 03-08-2003).]

Top
#136052 - 03/08/03 08:53 PM Re: Ground ring
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Lyle,
What is it that you call a Ground Ring?
What we have over here in NZ, is if a certain size of Mains is installed, the corresponding size of Main Earth is installed
also.
Bonding with Large Buildings, is done with multiple Earth Electrodes and welding of Bonding leads to Rebar sections, by Exo-thermic means.
With the advent of PE pipes, bonding of the water services, is not necessary.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#136053 - 03/09/03 03:39 PM Re: Ground ring
lyledunn Offline
Member

Registered: 06/30/02
Posts: 159
Loc: N.Ireland
Trumpy,

Interesting point you make re PE pipes. However, it is common practice for the water supply to be plastic and the internal plumbing to be copper. In this situation we are required to effect a main bond.
_________________________
regards

lyle dunn

Top
#136054 - 03/09/03 03:41 PM Re: Ground ring
lyledunn Offline
Member

Registered: 06/30/02
Posts: 159
Loc: N.Ireland
Paul,
What about supplies to "gas" stations in US system?. As you may be aware TNCS type supplies are not allowed in petrol filling stations in UK.
_________________________
regards

lyle dunn

Top
#136055 - 03/10/03 02:36 PM Re: Ground ring
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Yes, I was aware that filling stations in the U.K. are prohibited from using the PME system, although I've never had to work in such an environment.

In the U.S., chapter 5 of the NEC covers "Special occupances" and it would appear to me that gas stations would be covered by article 514. I've browsed through it quickly, but I can't see anything in it which changes the standard American TN-C-S equivalent supply system.

I'm sure we must have some Stateside members who could provide some more details? Is there anything in any other NEC sections which might apply here, guys?

Top
#136056 - 03/10/03 08:58 PM Re: Ground ring
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Lyle,
We still use Copper water pipes, over here,
like you said, we have to Bond and Earth all metallic pipework, makes sense though.
I once saw a Plumber cut a copper pipe and recieved a shock between the two cut pieces, must have been a small fault in the wiring in the house, where we were working.
He should have had a wire between both sides of his cut, but it gave him (and me) one H**l
of a fright