#13513 - 09/06/02 04:07 AM AFCI protecting smokes?
tsolanto Offline
Member
Registered: 09/03/02
Posts: 131
Loc: Long Island NY
If your going by the 2002 code, smoke detectors in bedrooms would be protected by AFCI, this does not sit right with me. In theory if someone was to unplug a lamp under load the AFCI should trip. If that were to happen the smoke detectors would not be live. We should not have to rely on the battery to save our lives. Most people don't check them anyway. I think smoke detectors should be able to be on a non AFCI circuit.

(B) Dwelling Unit Bedrooms. All branch circuits that supply 125-volt, single-phase, 15- and 20-ampere outlets installed in dwelling unit bedrooms shall be protected by an arc-fault circuit interrupter listed to provide protection of the entire branch circuit.
Top
Work Gear for Electricians and the Trades
#13514 - 09/06/02 02:54 PM Re: AFCI protecting smokes?
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
Quote:
In theory if someone was to unplug a lamp under load the AFCI should trip.


That would be a series arc, and one limited to a small value by the lamp. All the specifications that have been presented for AFCIs indicate that they will not trip on such a series arc.

(Uh oh.... Get ready for another rough ride! )
Top
#13515 - 09/07/02 03:53 AM Re: AFCI protecting smokes?
tsolanto Offline
Member
Registered: 09/03/02
Posts: 131
Loc: Long Island NY
So what are sucumstances to which they trip.
The local inspectors thought I had a valid point. I don't know what you mean small load from the lamp. that load would be way more than the minimum of 1 or 3 ma that I believe is rating for the AFCI
Top
#13516 - 09/07/02 06:58 AM Re: AFCI protecting smokes?
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
tsolanto,

The AFCI breakers are designed to ignore the type of situation you describe, just as it would ignore the internal arc in a switch that controlled a load as it was turned on and off. It is supposed to see these as "good arcs" and not bad ones.

Aside from that, there are many that agree with your thoughts about not including the smokes on the AFCI circuit.

I'm thinking I heard that Canada does not permit it. Electric-Ed; can you confirm that?

Bill
Top
#13517 - 09/07/02 08:35 AM Re: AFCI protecting smokes?
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
TS,
Apparently the AFCI is designed to trip only if it sees an arc of 75A or more over a period of several cycles, effectively limiting its usefulness to detecting parallel arcs in a 15 or 20A branch circuit.

The ground-fault protection incorporated is set at a level of 30mA, and you'll find many people on this board who are unhappy that the AFCI has been marketed on the basis that a series arc will trip the breaker when it eventually burns through the insulation and becomes a ground fault (or not, as the case may be).

This has really been a hot subject; if you do a subject header search on "AFCI" and another on "arc fault" you'll see plenty of threads.

Just to get you started, here's one of them.


[This message has been edited by pauluk (edited 09-07-2002).]
Top
#13518 - 09/07/02 03:56 PM Re: AFCI protecting smokes?
electric-ed Offline
Member
Registered: 07/08/02
Posts: 175
Loc: Canada
Bill, you are correct.
The CEC prohibits the installation of a smoke alarm on a circuit protected by a GFCI or an AFCI.

Ed
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals