We recently had a Shut-down in a local factory, to upgrade the 11kV/400V tranny,
after the work was done and the transformer was re-energised, I had the task of throwing the Main Isolator,(a heap of remedial work, had been done in the factory),and as I went to throw the switch,
(a 1000A ACB), it got stuck half-way,resulting in a flash and a bang!.
How do you guys feel about throwing High current Isolators?, personally they give me the Willies.
Your thoughts please?.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
#134645 - 11/24/02 04:57 AM Re: Main Switches
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
oh, you mean that first spark up...

.... depending on the x-former proximity, and impedance, the AIC could exceed your 'main isolator' ....not good.

personally, i position myself at arms length, look only as i position my left
(because i'm a righty), then look away and throw the switch/dico/main,etc..

even if the entire install has been gone over in detail, there could be a bad component (as was your Main Isolator?)

having been flashed hard sticks in your mind does'nt it??
Top
#134646 - 11/29/02 09:51 PM Re: Main Switches
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Sparky,
After I had replaced(Hooked Up), the DDO fuses, with all of the Isolators OFF, there was still a spark at the top terminal of the DDO's,(Xformer load), but we had a lot of new 400V gear, installed during the Shut-Down period, by other firms as well, I had to make sure that the people where ready for the power, to be connected, as it was not Locked Out, at their Isolator, as is required
by law.
But Sparky, I feel more comfortable, replacing a DDO fuse, than throwing a 1000A
Main Switch, at least you've got a certain amount of Manual control over a DDO fuse, if
it blows.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 57 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals