#13456 - 09/04/02 03:53 PM Outdoor Hot Tub
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
Is GFCI protection required for an outdoor hot tub. According to NEC 680.42 it does not appear it's a requirement. It refers to compliance to Part one and Part two of article 680 ie. permanently installed pools.
Top
Work Gear for Electricians and the Trades
#13457 - 09/04/02 04:47 PM Re: Outdoor Hot Tub
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Frank,

Check out 680.44, this applies to all installations. If you have the handbook, see the comentary following this section.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#13458 - 09/05/02 04:49 AM Re: Outdoor Hot Tub
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
Thanks Tom, that was good information I overlooked.

The situation I'm inquiring about is as follows: Residential outdoor hot tub located on a deck. It will be hard wired without the use of receptacles. The unit does not include GFCI protection. NEC 680.42 states outdoor installations shall comply with parts one and two of article 680 ie. permanantly installed pools. Based on that, my opinion is that GFCI protection is not required. However, bonding is required.
I'm just not certain if I'm interpreting the section properly.

Frank
Top
#13459 - 09/05/02 11:32 AM Re: Outdoor Hot Tub
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
IMO, 680.44 requires GFI protection for the your proposed installation.

The copy of the NEC that I have handy states that spa installations shall comply with parts I and IV, of which 680.44 is included.

The protection is required at the outlet (see definitions) & this doesn't matter if a receptacle is involved or not.

You might want to check into a Spa disconnect. These include a 50 amp GFI breaker in a NEMA 3R enclosure with separate neutral & equipment ground bus bars. Makes a neat job.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 95 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals