#13450 - 09/04/02 03:33 PM AFCI headache....has this ever happened to you?
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
Ok, here are the details....

Older home....New panel......New addition on the house. As required by code... a single 15amp AFCI breaker is placed on the circuit leading to the bedroom receptacles in the new bedroom in the new addition only....NOT the existing bedrooms of the older part of the house.

Here is the problem... no matter where the customer plugs something in any part of the house on OTHER circuits outside of the AFCI circuit (in the new section and the old section)....the AFCI trips!!

A bad AFCI breaker has been ruled out, as 5 have been replaced all with the same effect. I suspect a neutral back feed somewhere in the system. The Cutler-Hammer people have no answers....you guys have any ideas or seen/heard this problem before??


Sandro Parete www.santinoelectric.com

[This message has been edited by Sandro (edited 09-04-2002).]

[This message has been edited by Sandro (edited 09-04-2002).]
Top
Work Gear for Electricians and the Trades
#13451 - 09/04/02 05:11 PM Re: AFCI headache....has this ever happened to you?
eesparx Offline
Member
Registered: 01/21/02
Posts: 26
Loc: Colorado Springs, Colorado
You might want to check to make sure a ground and nuetral arn't touching somwhere in the circuit. If they are touching the AFCI will trip as soon as something is plugged in.
Top
#13452 - 09/04/02 06:12 PM Re: AFCI headache....has this ever happened to you?
electric-ed Offline
Member
Registered: 07/08/02
Posts: 175
Loc: Canada
Sandro, when you say "new panel" do you mean you installed a sub-panel for the new addition?
If so, did you bond the neutral to the new panel enclosure, or isolate it?

Ed
Top
#13453 - 09/04/02 06:32 PM Re: AFCI headache....has this ever happened to you?
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
I know this is a stupid question but did you connect the neutral wire from the new circuit to the neutral terminal on the arc-fault breaker or the neutral bar in the panel? Did you run 14-2 or 14-3 for your home run?

Curt
_________________________
Curt Swartz
Top
#13454 - 09/05/02 03:31 PM Re: AFCI headache....has this ever happened to you?
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
EESPARX.......thanks for the input.

Problem solved!!

Cheers!
Top
#13455 - 09/05/02 04:43 PM Re: AFCI headache....has this ever happened to you?
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
older BX circuitry folows suit many times.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 56 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals