#13450 - 09/04/02 06:33 PM AFCI headache....has this ever happened to you?  
Sandro  Offline
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
Ok, here are the details....

Older home....New panel......New addition on the house. As required by code... a single 15amp AFCI breaker is placed on the circuit leading to the bedroom receptacles in the new bedroom in the new addition only....NOT the existing bedrooms of the older part of the house.

Here is the problem... no matter where the customer plugs something in any part of the house on OTHER circuits outside of the AFCI circuit (in the new section and the old section)....the AFCI trips!!

A bad AFCI breaker has been ruled out, as 5 have been replaced all with the same effect. I suspect a neutral back feed somewhere in the system. The Cutler-Hammer people have no answers....you guys have any ideas or seen/heard this problem before??


Sandro Parete www.santinoelectric.com

[This message has been edited by Sandro (edited 09-04-2002).]

[This message has been edited by Sandro (edited 09-04-2002).]


Work Gear for Electricians and the Trades

#13451 - 09/04/02 08:11 PM Re: AFCI headache....has this ever happened to you?  
eesparx  Offline
Member
Joined: Jan 2002
Posts: 26
Colorado Springs, Colorado
You might want to check to make sure a ground and nuetral arn't touching somwhere in the circuit. If they are touching the AFCI will trip as soon as something is plugged in.


#13452 - 09/04/02 09:12 PM Re: AFCI headache....has this ever happened to you?  
electric-ed  Offline
Member
Joined: Jul 2002
Posts: 175
Canada
Sandro, when you say "new panel" do you mean you installed a sub-panel for the new addition?
If so, did you bond the neutral to the new panel enclosure, or isolate it?

Ed


#13453 - 09/04/02 09:32 PM Re: AFCI headache....has this ever happened to you?  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
I know this is a stupid question but did you connect the neutral wire from the new circuit to the neutral terminal on the arc-fault breaker or the neutral bar in the panel? Did you run 14-2 or 14-3 for your home run?

Curt


Curt Swartz

#13454 - 09/05/02 06:31 PM Re: AFCI headache....has this ever happened to you?  
Sandro  Offline
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
EESPARX.......thanks for the input.

Problem solved!!

Cheers!


#13455 - 09/05/02 07:43 PM Re: AFCI headache....has this ever happened to you?  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
older BX circuitry folows suit many times.