#134465 - 11/12/02 02:14 AM RCD's connections  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,211
SI,New Zealand
Please tell me, how would a switch-board mounted RCD or RCBO, be hooked up if you where connecting it up?.
Over here, we use a segregated Neutral busbar, for all of the load side Neutral conductors and the Lineside are connected to the Main Neutral Bus.
Your input please-
[Linked Image]


Let's face it, these days if you're not young, you're old - Red Green grin

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#134466 - 11/12/02 02:57 AM Re: RCD's connections  
C-H  Offline
Member
Joined: Sep 2002
Posts: 1,497
Stockholm, Sweden
Cut-and-paste from the instructions:

[Linked Image]

Or did you mean the other way around? Feeding an RCD from the switchboard?

[This message has been edited by C-H (edited 11-12-2002).]


#134467 - 11/12/02 11:07 AM Re: RCD's connections  
Hutch  Offline
Member
Joined: May 2002
Posts: 381
South Oxfordshire, UK
Exactly the same in South Africa. I think I've posted on this before but I cannot find it right now. GFCI required for all sockets and detached garage. Not required for lights, stove, water heater, hence two neutral busbars.


#134468 - 11/12/02 06:40 PM Re: RCD's connections  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
The same sort of split-neutral-bus panels have become common here as well. The RCD-protected circuit neutrals must be wired separately from the non-protected loads otherwise the breaker will just keep tripping.

A common arrangement here for new installations using TN-S or TN-C-S supply systems is for lighting and a couple of other "essential load" circuits, e.g. freezer/fridge or heating controls, to be on the line side and everything else to be fed through the RCD.

On TT systems that would necessitate the use of two RCDs. It's more usual to just see a single bus panel with a single main RCD on TT systems.


#134469 - 11/18/02 09:32 AM Re: RCD's connections  
Texas_Ranger  Offline
Member
Joined: Dec 2001
Posts: 2,392
Vienna, Austria
Simple thing in Austria: Main neutral directly to GFI/RCD, then wire links to 2pole breakers. With a 3ph setup (probably) 1 ph loads as described, neutral bus bar for 3 ph loads. If the panel is cheap (single pole breakers), neutral goes directly to the RCD, then to a neutral busbar.


#134470 - 11/24/02 12:46 AM Re: RCD's connections  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,211
SI,New Zealand
Thanks for your replies, there guys,
the new Wiring rules(referenced to Australia), require all circuits, exceptions
are Ranges and Water Heaters, to be protected by a 30mA RCD,exceptions are because of the leakage currents associated with these loads. [Linked Image]


Let's face it, these days if you're not young, you're old - Red Green grin


Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.002s) Memory: 0.7752 MB (Peak: 0.9211 MB) Zlib enabled. Server Time: 2017-03-23 00:17:43 UTC