#13444 - 09/04/02 12:34 PM Tap Conductors
tsolanto Offline
Member
Registered: 09/03/02
Posts: 131
Loc: Long Island NY
We were building a 400amp 3 phase service.
Out from the meter cabinet we went into a 400amp fused disconnect. From there we wanted to feed each of 2 Main breaker 200amp panels. My idea was to run 2 - 2" conduits, from the disconnect. one to each panel. the panels were 10 feet from the disconnect. I assumed that this could qualify as a tap. It's effectivly the same thing. The inspector violated it and said these were parallel conductors not a tap. I quoted 240-21D to no avail. Who is right?
Top
Work Gear for Electricians and the Trades
#13445 - 09/04/02 12:52 PM Re: Tap Conductors
electric-ed Offline
Member
Registered: 07/08/02
Posts: 175
Loc: Canada
The feeder conductors would have to be tied together at both ends in order to be in parallel.

Ed
Top
#13446 - 09/04/02 01:01 PM Re: Tap Conductors
tsolanto Offline
Member
Registered: 09/03/02
Posts: 131
Loc: Long Island NY
In response to electric-ed is it legal to do the install the way I described it
Top
#13447 - 09/04/02 01:22 PM Re: Tap Conductors
electric-ed Offline
Member
Registered: 07/08/02
Posts: 175
Loc: Canada
I am not sure of the NEC tap rules, as I live in Canada, but here it would be legal if- 1. the 200 amp feeder has an ampacity not less than the amp rating of the panel it feeds, and not less than the computed loads on that panel, and
2. it is not more than 10 ft. long, and
3. it is in non-ventilated raceway, or MC cable.

I would wait for a response from someone who knows the NEC on this.

Ed

[This message has been edited by electric-ed (edited 09-04-2002).]
Top
#13448 - 09/04/02 03:59 PM Re: Tap Conductors
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Tsolanto, your installation is legal. The inspector is wrong. These are two seperate loads and per your discription you are in compliance with tap rules.

I don't have a clue as to how he could consider two sets of conductors going to different points could be paralleled.

If it would make him feel any better, you could scrap the 400 amp disconnect and use parallel lugs on the load side of the meter, or replace it with a gutter and simply splice 3\0 CU conductors to your 400 amp conductors here.

Given the location of these panels, this would be in compliance with articles 230 and 240.


Roger

[This message has been edited by Roger (edited 09-04-2002).]
Top
#13449 - 09/04/02 06:42 PM Re: Tap Conductors
Electric Eagle Offline
Member
Registered: 04/20/02
Posts: 914
Loc: Alpharetta, GA
Sounds like your installation is code compliant from what you've stated. I would copy art. 230.46 and 240.21 and the Webster's dictionary definition of parallel and ask the inspector to re-evaluate his conclussion.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 14 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals