The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 340 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#13375 - 09/02/02 09:36 AM Fire or safety concerns about receptacle loads
Elzappr Offline

Registered: 12/20/01
Posts: 273
Loc: Oregon
Art 210 requires stationary equipment that takes up 50% of a circuit's capacity to be a dedicated circuit. Other than engineering or usage convenience considerations, is there a safety issue? I recently had to repair a damaged installation that apparently was modified by a maintenance person AFTER initial construction, so that it violated the 50% rule. They tapped into a large role up door opener (in a commercial building) to provide power for a couple of convenience outlets. I don't like driving customers away by re-engineering existing installations because of code issues which aren't obvious safety issues. Anyone have some perspective about what is so dangerous about violating the 50% rule?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#13376 - 09/02/02 12:41 PM Re: Fire or safety concerns about receptacle loads
sparky Offline

Registered: 10/18/00
Posts: 5545
the fallicy is, that anyone can 'dedicate' a circuit without consultation......

#13377 - 09/02/02 12:45 PM Re: Fire or safety concerns about receptacle loads
pauluk Offline

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
As I see it, the problem with violating such a rule would be that if/when other high-power appliances are connected to the circuit, there could be a high incidence of nuisance tripping.

That in itself wouldn't be a problem so long as the OCPD and cables are properly sized. The only real safety issue I can see is that regular nuisance trips might lead to some uninformed person deciding to uprate the breaker in order to "solve" the problem. Then it could most definitely be a safety problem.