#13310 - 08/30/02 05:50 PM smokes
elecbob Offline
Member
Registered: 08/23/02
Posts: 141
Loc: WA
I've made it a practice to install smokes on a dedicated 15 amp (#14) circuit. It isn't required by code but it seemed like a good idea to me. Anyone else here feel the same?
Bob
Top
Work Gear for Electricians and the Trades
#13311 - 08/30/02 05:53 PM Re: smokes
Electric Eagle Offline
Member
Registered: 04/20/02
Posts: 914
Loc: Alpharetta, GA
That's the way we do it also.
Top
#13312 - 08/30/02 06:04 PM Re: smokes
N.O.Minded Offline
Member
Registered: 01/14/02
Posts: 10
Loc: Pensacola,FL-USA
elecbob,
IMHO, They should be put on a dedicated branch circuit due to endless possibilities/scenarios that could arise causing failure of these life safety devices.
However, in my area the AHJ has adopted the 2002 which require the smokes to be on AFCI if located in Bdrm. Therefore the cost effective method thus far has been to include them on one of the Bdrm AFCIs. BTW,JMHO
Regards, Andrew
Top
#13313 - 08/30/02 06:11 PM Re: smokes
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Many areas have rules that prohibit smoke detectors from being on their own dedicated circuit. The are required to be put on a commonly used circuit so that if the circuit was off for any reason, action would be taken to restore power to the commonly used circuit and the detectors.
Don
_________________________
Don(resqcapt19)
Top
#13314 - 08/30/02 06:17 PM Re: smokes
electric-ed Offline
Member
Registered: 07/08/02
Posts: 175
Loc: Canada
I believe Smoke Alarms should be supplied from a lighting circuit so that there is less chance of the supply being inadvertantly shut off, and not noticed.

Ed
Top
#13315 - 08/30/02 07:21 PM Re: smokes
elecbob Offline
Member
Registered: 08/23/02
Posts: 141
Loc: WA
I guess any fire serious enough to cause a breaker trip on a lighting circuit would first be detected by the smokes so maybe the argument that they should be shared with something that would alert occupants that there is a problem with the circuit is valid. Recently, in a duplex I fed them from a dedicated circuit off of the seperate house panel feeding the basement. The inspector said nothing. Regarding AFCI's: I thought only outlets in bedrooms needed protaction. Do smokes and lights need protaction too? What about dedicated HVAC receptacles (including 120/240 volt) in bedrooms?
Thanks
Bob
Top
#13316 - 08/30/02 10:08 PM Re: smokes
ElectricAL Offline
Member
Registered: 10/10/01
Posts: 597
Loc: Minneapolis, MN USA
Quote:
210.12 Arc-Fault Circuit-Interrupter Protection.

(B) Dwelling Unit Bedrooms. All branch circuits that supply 125-volt, single-phase, 15- and 20-ampere outlets installed in dwelling unit bedrooms shall be protected by an arc-fault circuit interrupter listed to provide protection of the entire branch circuit.

Quote:
Definition.
Outlet. A point on the wiring system at which current is taken to supply utilization equipment.

An example is a lighting outlet, a receptacle outlet, smoke detector outlet, 15 or 20 A, 125 V AC outlet, etc.
_________________________
Al Hildenbrand
Top
#13317 - 08/30/02 11:01 PM Re: smokes
elecbob Offline
Member
Registered: 08/23/02
Posts: 141
Loc: WA
Thank you for the clarification ElectricAL. The electrical inspecters around here have certainly been lax in their enforcement on AFCI's.
Bob
Top
#13318 - 08/31/02 12:56 PM Re: smokes
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
They cost more, and seem to come fitted with the cheapest of 9V battery, but apparently some NorCal jurisdictions require combination AC- and DC-powered detectors. Maybe a ‘value-added’ homeowner-optioned adder for new construction?
Top
#13319 - 08/31/02 02:02 PM Re: smokes
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Al,
How do I find a current and voltage rating on an "outlet'???
Don
_________________________
Don(resqcapt19)
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 40 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals