#130819 - 03/08/07 04:32 PM Metal Halide Lights
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
Installing 2 - 400 watt metal halide lights per pole. 4 parking lot lights in an existing light poles. Can I go with 3-400 watt lights per 20 amp 120 volt circuit? Do I need to allow for the tranformer in the light?
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
Tools for Electricians:
#130820 - 03/08/07 06:25 PM Re: Metal Halide Lights
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
This question sounds very familiar, but nevertheless here is my $0.02:

Use the listed Line Input Amperes for the Fixture or Ballast, which will reflect the computed VA Load value for a given Fixture.

This information may be found either on the Ballast's Nameplate, the Fixture's Nameplate, or from Cutsheets for the Fixture and/or a Ballast Manufacturer.

Typically, for any common Guesstimation, if the Ballast kit includes a Capacitor + is listed as "HPF" (High Power Factor), then the PF is somewhere in the 0.8 region.

A 400 Watt HID Ballast / Lamp assemblage with 80% Power Factor, should draw 4.0 Amps at 120 VAC during normal operation.

If the Ballast is CWA (Constant Wattage Autotransformer), the 4.0 Amps should remain somewhat steady from initial starting of the Lamp, throughout the normal operation; meaning:
* There should not be any high starting current demands to consider (some starting current demands may be in excess of 200% the stable operating current rating).

So, if a given Fixture draws 4.0 Amps at 120VAC, and you plan to install Three (3) Fixtures per 20 Amp Circuit, the "Subtotal" Load Current per Circuit would be 12.0 Amps.

Add 25% for LCL (unless these Lights will be on for less than 180 minutes at a time), and the resulting per-circuit designed load is 15 Amps per 20 Amp Circuit.

This conforms to the minimal NEC requests for using #12 with 20 Amp OCPD, and applying an LCL derating factor.

As always, verify that there will not be excessive Voltage Drop issues, as the HID Lamps may cycle excessively, or Ballasts may be damaged - or both.

Let me know if I did not address your question correctly, or if you have additional questions.

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#130821 - 03/13/07 04:45 PM Re: Metal Halide Lights
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
aldav53 ,

Did this information help?

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (annemarie1), 67 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals