The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 198 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#130785 - 02/05/07 10:07 AM Watt/KVA
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
How close is KVA to wattage when reading on a transformer or machine, etc.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#130786 - 02/05/07 10:10 AM Re: Watt/KVA
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
It depends on the power factor, which depends on the load. Generally speaking, PF is between 0.8 and 1 which means kW is 80-100% kVA. But this isn't always the case; you may be able to calculate it based on nameplate data, but it ultimately will require a measurement to know for sure.

Top
#130787 - 02/05/07 10:26 AM Re: Watt/KVA
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
So the PF would be different according to the load and/or if its a 120/208 or 277/480v.
if that makes sense
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#130788 - 02/05/07 06:48 PM Re: Watt/KVA
WFO Offline
Member

Registered: 09/03/05
Posts: 206
Loc: Cat Spring, TX
The voltage would not determine the power factor.

Top
#130789 - 02/05/07 07:05 PM Re: Watt/KVA
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
This is for a 400 volt machine 3 ph 63 amp.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#130790 - 02/05/07 10:05 PM Re: Watt/KVA
ScubaDan Offline
Member

Registered: 08/23/06
Posts: 21
Loc: Sacramento, CA, USA
It might help to review the power triangle to see the relationship of Real Power(P), Apparent Power(kVA) and Imaginary Power(kVAR).

The angle opposite the Imaginary Power side is known as the angle of phase offset, of which its cosine is power factor.

Top
#130791 - 02/07/07 01:32 PM Re: Watt/KVA
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
Here is a simple example of the Power Triangle, which will assist with the Power Factor conclusion:
(it also doubles as the Basic Impedance Triangle, and the Basic Pythagoris Theorym)

============================================

4 Watts (True Power),
3 VARs (Reactive Power),
5 VAs (Apparent Power).

============================================

Power Factor = 0.8 (80%) lagging
4 Watts is 80% of 5 VA.
---------------------------------------------

Some detail to these items:

*** WATTS ***
Watts = True Power,
KW = Kilo Watts = 1,000 Watts;

*** VA ***
VA = Volt-Amps = Apparent Power = Reactive Power and True Power compiled,
KVA = Kilo Volt-Amps = 1,000 Volt-Amps = 1,000 VA;

*** VAR ***
VAR = Volt-Amps Reactive = Reactive Power = Scuttle Power,
KVAR = Kilo Volt-Amps Reactive = 1,000 Volt-Amps Reactive = 1,000 VAR.

In the example values listed above, the preceeding relate to listed Trigonomic Terms:




    [*] 4 Watts = "Sine" (Base of the Triangle),


    [*] 3 VARs = "Cosine" (Opposite side of Triangle),


    [*] 5 VAs = "Tangent" (Hypotenuse)


You can use this formula to find any single unknown value, as long as you have two known values.

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#130792 - 02/11/07 07:24 PM Re: Watt/KVA
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
Bump....

Any update on this?
(Did the examples make sense + help?)

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#130793 - 02/12/07 03:40 AM Re: Watt/KVA
LarryC Offline
Member

Registered: 07/05/04
Posts: 776
Loc: Winchester, NH, US
Scuttle Power?

Is that supposed to mean the "power" that is scuttling back and forth between the load and the source, that doesn't do any real work, but requires us to upsize conductors and such, in order to accommodate its journey?

Larry C

Top
#130794 - 02/12/07 09:07 AM Re: Watt/KVA
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
I've never heard the term 'scuttle power', but seeing as how it is used as a synonym for reactive power, then 'power going back and forth between source and load' is exactly how I read it.

If you look at a sinusoidal load with a power factor less than 1, you will find that the sine wave representing current is not in phase with the sine wave representing voltage. This means that there will be portions of the AC cycle in which current has one polarity, and voltage the other, meaning that the load is supplying power back to the source. Over the entire AC cycle, the net power delivery is from source to load, but over part of the cycle there is a reverse flow of power.

-Jon

Top