The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 327 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#130742 - 12/01/06 05:46 AM Max current load
JakeJ1 Offline
Junior Member

Registered: 03/24/05
Posts: 3
Loc: charleston SC USA
Not necessarily an NEC/code question. If I have two 10Awg circuits using 10/3 with ground MC cable and I put these together in parallel, what is the max current load that this will support?

#130743 - 12/01/06 07:13 AM Re: Max current load
sabrown Offline

Registered: 12/12/02
Posts: 297
Loc: Ogden, Utah, USA
Article 310.4 discusses conductors in parallel. Using the information there we find that paralleling #10 is only allowed in limited circumstances and based on Exception 1 (b) we find that parallel #10 (referring to table 310.16) carry 30 amps at 60 degree C (no increase in ampacity).

#130744 - 12/01/06 08:25 AM Re: Max current load
JakeJ1 Offline
Junior Member

Registered: 03/24/05
Posts: 3
Loc: charleston SC USA
Thanks for the prompt reply. I find it interesting that the overall ampacity will not increase when two like cables are placed in parallel.

Thanks again..

#130745 - 12/01/06 01:34 PM Re: Max current load
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
That is not always the case.

2 cables with 1/0 or larger conductors will have double the ampacity. 3 cables with 1/0 or larger will have triple the ampacity.

In general there is little benefit from paralleling conductors smaller than 1/0 and you can only do it for specific installations.
Bob Badger