The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 106 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#130728 - 11/11/06 11:14 AM Variable transformer
ayrton Offline
Member

Registered: 12/21/01
Posts: 205
Loc: Pa
I am not familiar with these. Is it safe to assume it regulates voltage?
Running through the center of the three coils is a shaft, and attached to the top of the shaft are gears which drive a chain. I am not sure what it is doing.

The nameplate on the housing reads 'Input V 240 Hz 50-60 Ph3 Output V 0-280 Amps 250 KVA 121.

Now to calculate what this thing should be fed with, I usesd the formula KVAx1000/ Voltage (240) 121x1000=121000/240=504.16

They are feeding this with a Nema5 starter using 2/0 wire. If I am calculating right, shouldnt the ampacity of the wire be based on 504?

This variable transformer than feeds an oil filled transformer with output votages as high as 36kv.

It is in a drywalled room in an office suite. According to art 450 I beleive it needs to be in a vault.

But there are 7 exceptions. I do not know the KVA of the second tranformer.

Please help!

Top
#130729 - 11/11/06 09:00 PM Re: Variable transformer
Bob Offline
Member

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA

Top
#130730 - 11/12/06 05:46 AM Re: Variable transformer
ayrton Offline
Member

Registered: 12/21/01
Posts: 205
Loc: Pa
Thank you Bob. That was informative. I still am not sure on the feeder size.
Who can tell me if I am right when using the formula?
121kva @240v is 504amps. This is currently wired with 2/0

Top
#130731 - 11/12/06 05:58 AM Re: Variable transformer
LarryC Offline
Member

Registered: 07/05/04
Posts: 776
Loc: Winchester, NH, US
 Quote:
121kva @240v is 504amps


If you are single phase.
---------------------------------------------------------
But since you are three phase

KVA = V x A x sqr rt 3

KVA/(V x sqr rt 3) = A

121000/(240 x 1.73)= 291

Top
#130732 - 11/14/06 01:39 AM Re: Variable transformer
jraef Offline
Member

Registered: 07/21/04
Posts: 91
Loc: San francisco, CA, USA
Yes, but if the nameplate says 250A, it is 250A. That needs to be the basis for your fusing, so the wire need only be sized for the fused circuit.
_________________________
JRaef

Top
#130733 - 11/14/06 04:00 AM Re: Variable transformer
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
At the maximum voltage level of the transformer:

121kVA = 280V x 250A (3P).

To set the OCP for 291A @ 240V would allow the transformer to overload if it was adjusted to 280V. If this were a normal transformer and you could lug it to the 240V terminals, OCP can be sized for 291A, but in this case, 250A is required for safety.

[This message has been edited by SteveFehr (edited 11-14-2006).]