#130721 - 10/28/06 05:21 AM Protective Relays with no ADC
Alexander Boyko Offline
Junior Member
Registered: 10/22/06
Posts: 2
Loc: Krasnoyarsk, Russia
Hi

I wonder is there any technology that allow to transmit measured data from CT and VT in a digital form to a protective terminal with no copper, via Ethernet or something.

Is there any protective terminals with a digital measuring inputs?

Is there any CT and VT with a digital output (not optical CT and VT)

Thanks.
Top
Tools for Electricians:
#130722 - 11/01/06 07:30 PM Re: Protective Relays with no ADC
Dave T Offline
Member
Registered: 01/22/05
Posts: 155
Loc: Waukesha, WI, USA
I believe it may be able to done to monitor but not to provide protection. It is imperative that a protective system be fail safe if ti configuration as you have described implies that you are looking for wireless protection as was stated: "digital form to a 'protective terminal' with no copper, via Ethernet or something."
Top
#130723 - 11/02/06 02:49 AM Re: Protective Relays with no ADC
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
I'm not sure I understand your need very clearly, but if your looking to monitor your inputs, and transmit that data wirelessly, or via the ethernet, this would work.
http://www.electroind.com/shark100s.html
Top
#130724 - 11/02/06 04:58 AM Re: Protective Relays with no ADC
Alexander Boyko Offline
Junior Member
Registered: 10/22/06
Posts: 2
Loc: Krasnoyarsk, Russia
Thanks

I am talking bout delivering measurements in a digital way from CT to relay in oreder to protect a line, transformer etc.

I believe I had seen some info bout such experemental substation before, but now cannot find it.

My article bout these kind of things is going to be published in a magazine, so I am looking for practical appliances. And I am sure to remember that I have seen ones.
Top
#130725 - 11/02/06 05:26 AM Re: Protective Relays with no ADC
BugMan Offline
Member
Registered: 08/24/06
Posts: 10
Alex,

There are many ways to transfer protective digital info. Presently, most utilities are going to fibre, since the high EMF during fault conditions has no affect on the signal being transmitted. The fiber signal is also reliable enough for protection of xfmrs, transmission lines, buses, etc because the devices used to transmit the signal through the fiber have a self-monitoring scheme built in. The protection digital signal can travel over a 100 miles through single-mode fiber. If you feel froggy, you can check all you want at Schweitzer Engineering Labs (SEL) at www.selinc.com. Have fun reading.

[This message has been edited by BugMan (edited 11-02-2006).]
Top
#130726 - 11/11/06 07:14 PM Re: Protective Relays with no ADC
WFO Offline
Member
Registered: 09/03/05
Posts: 202
Loc: Cat Spring, TX
Top
#130727 - 11/13/06 07:58 PM Re: Protective Relays with no ADC
BugMan Offline
Member
Registered: 08/24/06
Posts: 10
Careful. Many of the optical xdcrs are experimental. And, much is unknown on how they behave under fault conditions with high X/R ratios, lightning, etc.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 63 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals