The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (cableguy619), 314 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#13067 - 08/23/02 04:54 PM Short circuit and water main leak connected?
GRex Offline
Junior Member

Registered: 08/23/02
Posts: 1
Loc: Rochester, MN, USA
I had some central AC installed in my attic recently, and a short circuit (or some event) occurred when one of the two 240V circuits were switched on. The circuit breaker did not trip; the installer had to manually switch the circuit off to stop the event. The lightbulbs dimmed in the house, my cable TV was fried, and I noticed what turned out to be a leak in my main water pipe under the foundation.

I have a boiler system for heating, and I'm thinking the short circuit leaked current across my boiler pipes and arced over to the water line and poked a hole in it.

I've been told that this is possible, but I'd like to know for sure.

Any ideas?


Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#13068 - 08/24/02 03:39 AM Re: Short circuit and water main leak connected?
pauluk Offline

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Another possibility might be that if the current flowing through the pipework was very high, it could have heated it enough to melt a soldered joint.

#13069 - 08/26/02 08:09 AM Re: Short circuit and water main leak connected?
strangedog Offline

Registered: 08/23/02
Posts: 30
Loc: Dayton, Ohio
It sounds to me like you have some grounding issues. Perhaps grounding rods and ther water pipe ground are not bonded together, or no grounding rods at all (older service). The cable blew due to the current flowing through the pipe going to the cable bonding nut and through the cable box (and back down the ground wire probabally).

I would say you have at least 2 problems:

1) High resistance gound (does not allow enough current to flow to trip the breaker.

2) Bonding problems. All grounds are supposed to be bonded together to create an equal potential. Improperly bonded grounds will easily destroy electronic equipment (cable sattilite system, computer networks etc) as they use and link grouns on different points in the electirical system.

It is best for a leader to be both feared and loved. But since this usually cannot be done, it is safer to be feared.