#13060 - 08/23/02 02:47 PM transfer switch
derater Offline
Member
Registered: 03/30/02
Posts: 179
Doing generator/panel transfer switch tomorrow, 200a res.,Never did one and my partner(who has) can't be there.Any tips?
Top
Work Gear for Electricians and the Trades
#13061 - 08/23/02 03:24 PM Re: transfer switch
George Corron Offline
Member
Registered: 05/16/01
Posts: 717
Loc: Lorton, Va USA
De-
They're fairly self explanatory, read the instructions (sorry, I know that's NOT the electrical way ) it's pretty much Normal line in, Line out, Emergency line in. You didn't say manual or automatic, auto means you have a start signal to genset, transfer signal from source to contact (which is sometimes pre-wired). You'll do fine, take a deep breath, another drink of coffee, and dig in.
Top
#13062 - 08/23/02 03:51 PM Re: transfer switch
go-go Offline
Member
Registered: 08/08/02
Posts: 42
Loc: Fla.
Top
#13063 - 08/24/02 04:57 AM Re: transfer switch
electric-ed Offline
Member
Registered: 07/08/02
Posts: 175
Loc: Canada
Make sure you have the correct transfer switch for the type of generator being installed.

If the generator neutral is bonded to the frame by the manufacturer, a transfer switch that breaks the neutral (three pole) is required.

Here is a basic diagram for a typical generator with a bonded neutral.



However, if the generator neutral is not bonded to the frame, a transfer switch with a solid neutral buss (two pole) is should be used.

Here is the basic diagram for a typical generator with a floating (not bonded) neutral.



Hope this helps,

Ed
Top
#13064 - 08/24/02 05:20 AM Re: transfer switch
scjohn Offline
Member
Registered: 07/04/02
Posts: 74
Loc: charleston, SC, USA
ElectricEd, is the use of the 3 pole switch to protect the generator, or the lineman? I have installed a couple of these and have always thought that breaking the neutral would seem the safest for the lineman. The people at Ronk swear that you only need a single pole switch in a single pole application, not to mention the extreme difference in price. What do you think?
Thanx, John
Top
#13065 - 08/24/02 05:36 AM Re: transfer switch
electric-ed Offline
Member
Registered: 07/08/02
Posts: 175
Loc: Canada
No, John. The neutral must be switched to prevent the equipment bonding conductor (EGC) from being in parallel with the neutral in installations where the generator neutral is bonded to the frame.
This would permit the neutral (unbalanced) current to flow on the EGCs which is a NEC violation.

Note also that in these cases, where the neutral is switched, the generator neutral is required to be earth grounded.

Ed

[This message has been edited by electric-ed (edited 08-24-2002).]
Top
#13066 - 08/25/02 05:42 AM Re: transfer switch
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Ed,

Again, great work on the Schematics!!!

Scott S.E.T.
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 36 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals