#130551 - 07/22/06 10:02 AM Residential Device Termination Best Practice Question
hodger Offline
Junior Member
Registered: 02/14/05
Posts: 2
Loc: Austin
Hello all:

I am interested in this forums opinions on the pro's and con's of "stabbing" wires into back of devices versus "screwing" down. As of now, our company use the screw method, but more and more over the years we are seeing this as the abnormal practice in our area.

Does it make since to continue to take the extra time to do this on our trim outs?
_________________________
rick
Top
Tools for Electricians:
#130552 - 07/22/06 11:08 AM Re: Residential Device Termination Best Practice Question
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
I have seen way to many poor connections and burned up wires to trust the backstab terminations. I always use the screw terminals, or better yet the screw down "pressure plate" type found on high quality devices.
Top
#130553 - 07/22/06 03:19 PM Re: Residential Device Termination Best Practice Question
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
I was taught not to back wire in the 70's. I have not seen anything to convince me that it is a good idea. When you twist the wire around the screw and tighten down, I think your contact area is a little more certain.
Joe
Top
#130554 - 07/24/06 03:07 PM Re: Residential Device Termination Best Practice Question
VAElec Offline
Member
Registered: 07/26/05
Posts: 49
Loc: Sterling, Virginia, US
I love the "pressure plate" type termination. Back stab ease, but you still screw it down. Have found both backstab, and hook it and screw it down type devices burned up. I think if you avoid cheap devices, the termination style does not matter to a huge degree.
_________________________
Pete
Top
#130555 - 07/24/06 07:43 PM Re: Residential Device Termination Best Practice Question
Celtic Offline
Member
Registered: 02/26/05
Posts: 361
Loc: NJ
Have you ever stabbed a breaker?
I think that speaks volumes on the subject.
_________________________
~~ CELTIC ~~
...-= NJ =-...
Top
#130556 - 07/24/06 11:28 PM Re: Residential Device Termination Best Practice Question
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
celtic:

How about those horrible Zinscos with the quick release?

I think I have a few in my junk pile.
_________________________
Stupid should be painful.
Top
#130557 - 12/24/06 08:57 AM Re: Residential Device Termination Best Practice Question
Obsaleet Offline
Member
Registered: 04/05/03
Posts: 362
Loc: Pa
I personnally love the stab in the back................they keep me in business. Garuanteed service calls in the waiting. Usally the 1st device on the circuit stab fails when the load side devices are loaded up. Space heater on the last device and a couple of lamps and boom a service call for no power, power keeps going on and off, burned device, open neutral, etc.
Ob
_________________________
Choose your customers, don't let them choose you.
Top
#130558 - 12/24/06 09:07 AM Re: Residential Device Termination Best Practice Question
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I think a sure fire way to make a stab fail is to have the wire less than perfectly straight when you stab it.
_________________________
Greg Fretwell
Top
#130559 - 12/24/06 09:14 AM Re: Residential Device Termination Best Practice Question
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Quote:
Have you ever stabbed a breaker?


Yes.

Somewhere on this site I have a picture of a QO twin breaker with speedwire terminals.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#130560 - 01/04/07 08:52 PM Re: Residential Device Termination Best Practice Question
tdhorne Offline
Member
Registered: 03/22/01
Posts: 345
Loc: Maryland, USA
Quote:
quote:Have you ever stabbed a breaker?

Yes.

Somewhere on this site I have a picture of a QO twin breaker with speedwire terminals.

Iwire
Say it aint so. QOs with back stabs. That's it the world has officially gone to hell.
--
Tom Horne
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 53 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals