The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 101 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#130422 - 04/13/06 05:35 AM operation of 225kVA static UPS - ISSUES WITH HARMONICS
vmac100 Offline
Junior Member

Registered: 10/25/04
Posts: 4
Dear All,
please, we have an electrical power supply installation to one unit of Balanced Power Plus 225kVA static UPS machine and two 75kW pumps. All three equipment are supplied power from the same busbar. We propose to install dual soft start panel to replace the existing dual star-delta panel that is presently used to power the pumps from the 415V LV busbar. The pumps are 3-phase.

However, we will like to know if we are going to be experiencing problems with harmonics when the pumps are running after we have installed the soft-start panel. We wish to know if this panel upgrade will cause an increase in the Total Harmonic Distortion (in current and voltage) and what the effect on the UPS will be. Also, we will like to know if there are equipment that we can install that will limit the THD to acceptable values (for the UPS) when the pumps are running.

Do treat as urgent and thanking you for your co-operation and support.

Top
#130423 - 04/15/06 08:25 PM Re: operation of 225kVA static UPS - ISSUES WITH HARMONICS
Bob Offline
Member

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA

Top
#130424 - 04/27/06 09:37 PM Re: operation of 225kVA static UPS - ISSUES WITH HARMONICS
Erloq Offline
Junior Member

Registered: 10/07/05
Posts: 6
Loc: Concord,CA,USA
Quick question...
A 225kVa UPS is a double conversion device and rather immune to terrible input power. Are you concerned about THD PoCo penalties?
Other than a active injection filter, voltage and current distortion will vary too much at startup and full load to be resolved by a static or tunned filter. Personally I wouldn't worry much about the UPS.
The UPS has already been exposed to mild/moderate surge and transients with the wye/delta starters. The EFI MOV's are typically the weakest link on the input of most UPS's.
_________________________
Eric

Top