The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 101 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#130384 - 03/20/06 02:34 PM Load Calculations
rhpope Offline
Member

Registered: 02/23/06
Posts: 18
Loc: North Carolina
When calculating the load for a building, how do you spread the single and three phase loads over the incoming three phase lines? I belive the correct way for 120/208 Wye is that single phase 208 or 240 loads spread equally across two transformers (A&B, B&C, or C&A) whereas for 120/240 Delta, 208 or 240 single phase load is applied to only one transformer (A, B, or C)/phase (just as the 120 loads are only on the A & C phases). The three phase loads are spread equally across all three phases.

Top
#130385 - 03/20/06 05:18 PM Re: Load Calculations
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
You seem to have it correct. The only thing that's really tricky is that, on a delta with a high leg (B phase), any load that has a neutral connection, i.e., 240/120 or just 120, must be connected only to the other two phases (A or C), as you noted.

Typically, the high-leg delta system has less load on B phase than the other two, because only line-to-line or 3-phase loads are served by this phase, whereas A nd C phases serve all of the line-to-neutral loads.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#130386 - 03/20/06 06:39 PM Re: Load Calculations
Dnkldorf Offline
Member

Registered: 12/12/04
Posts: 1091
Loc: nowhere usa
I agree with your thinking about spreading the loads as equally as you can, which would be balancing of the transformer.

Using a 208/120Y transformer you can use any of the phases for 120V loads, any 2 of the phases for single phase 208V loads and all three for 3 phase 208V loads. However you can't use any combination of these for 240V loads...

Using a 240/120 Ct transformer, you can use A or C phase for 120V loads, any 2 phases for single phase 240V loads, and all 3 for 3 phase 240V loads. You can't use any combination for 208V loads....

Mind you with this type setup and using the high leg, you must be concerned about using full voltage breakers where with the 208/120Y setup, the use of "slash" breakers could be used.


Dnk...