The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 202 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#13012 - 08/22/02 06:09 PM Ufer in dirt
Cindy Offline
Member

Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
would you find this acceptable? [instead of stubbing the ufer up through the foundation wall 12" above the bottom plate indoors,] stub the Ufer rebar out of the footing, outdoors exposed to the dirt and weather, with a typical ground rod connection made to this Ufer. pipes, conduits, and rods can be iron or steel, if the conditions are met in 250, but it seems to me that rebar doesn't really fit outdoors in a wet environment. i would expect it to rust and lose its value at the acorn or clamp connection. but we allow clamps to bond to galvanized water pipes and black iron gas lines outdoors, and you are supposed to scrape the coating off to make a good bond. go figure.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#13013 - 08/22/02 07:47 PM Re: Ufer in dirt
nesparky Offline
Member

Registered: 06/21/01
Posts: 650
Loc: omaha,ne
When we use the rebar as an ufer we clamp a piece of #4 bare copper onto the rebar and run it to the service location.
_________________________
ed

Top
#13014 - 08/22/02 08:01 PM Re: Ufer in dirt
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
I have to ask; what is a "ufer"???

HotLine1
John
_________________________
John

Top
#13015 - 08/22/02 09:08 PM Re: Ufer in dirt
Cindy Offline
Member

Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
ufer = concrete encased electrode

Top
#13016 - 08/22/02 09:55 PM Re: Ufer in dirt
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
Cindy

I would have a hard time accepting the exposed ufer connection for the reasons you are concerned about. As far as other piping I have never been required to scrape the galvanized coating off water piping and doing so would cause the plumber and plumbing inspector to have a fit. Black iron gas piping and fittings are not supposed to be installed where they are exposed to weather unless they are coated for protection. Again it would be a violation to remove any protective coating.

I would also not permit an acorn clamp to used to connect the grounding electrode conductor to the ufer. I have never seen one listed for this purpose and doubt there are any. Copper and steel should never be in direct contact with each other because of electrolysis. I don't have a problem with using standard brass or bronze clamps even thought most are also not listed for this purpose. I know most of the T&B U-bolt type ground clamps are listed for rebar.

Curt
_________________________
Curt Swartz

Top
#13017 - 08/23/02 03:39 AM Re: Ufer in dirt
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
i stub out the cu in pvc. should i assume the effort here is in keeping a continuous GEC?

'fingers' i'm told disipate a strike better than a single line (ampacity divides..) there is even a 'crow's foot' design for this...

here's a Ufer John, just did one @ 2200' on ledge.

Top
#13018 - 08/23/02 05:01 AM Re: Ufer in dirt
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
We must live in a different world here in So CA.
The AHJ's will only accept 20'or > of GEC sized (or larger) Cu as a Ufer.
When bonded to the rebar, I do it with Cadwelds.
Galvanized water lines? Haven't seen one in years, except on old buildings. Just Cu.

Top