The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129992 - 12/27/05 04:56 PM Impedance matching on transformer banks
WFO Offline
Member

Registered: 09/03/05
Posts: 206
Loc: Cat Spring, TX
First, I'm always getting asked by the linemen if they can bank an "X" impedance transformer with a "Y" impedance transformer. The old REA specs we have never even mention it except in the delta/delta configuration. So we (I) have always assumed that it doesn't matter in the wye/delta and wye/wye banks that we use. Is this true?

Secondly, when the REA specs DID refer to impedance balancing, they would say that the tansformers had to be within plus or minus "X" percent of each other. Were they referring to the "percent" as stamped on the nameplate, or an actual arithmetical percentage between the two (or three) values?

Top
#129993 - 12/28/05 10:31 PM Re: Impedance matching on transformer banks
Dave T Offline
Member

Registered: 01/22/05
Posts: 157
Loc: Waukesha, WI, USA
My notes state that the impedence of the transformers to be paralleled should be within 7-1/2% of each other so that they will share the load as close as possible.

Top
#129994 - 12/29/05 04:04 AM Re: Impedance matching on transformer banks
WFO Offline
Member

Registered: 09/03/05
Posts: 206
Loc: Cat Spring, TX
Sorry, I didn't really word my question that well. I didn't mean paralleling them, just operating them together 3 phase banks.

Top
#129995 - 12/29/05 12:37 PM Re: Impedance matching on transformer banks
Dave T Offline
Member

Registered: 01/22/05
Posts: 157
Loc: Waukesha, WI, USA
My application notes state that a D-Y bank would share equally a balanced 3ph load even though the impedance of the individual transformers may not be equal. That identical transformers should be used in D-D and open D banks. Also, Y-Y should be avoided.