The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 229 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129897 - 11/09/05 08:32 AM Voltage Drop Calculation
mhulbert Offline

Registered: 10/19/04
Posts: 133
Loc: Anaheim, CA USA
I have an instructor telling me that to do a VD calc, you use the following formula:
VD=(Amps x 1 way Length x R)/1000'

Where R = ohm/kFt from NEC Ch 9, Table 8

It seems to me like you would have to double the length since we are only counting the resistance in one this correct? I have always used the online calculators, and I'm trying to learn how to do it on paper.

Thanks, Mike

#129898 - 11/09/05 04:10 PM Re: Voltage Drop Calculation
winnie Offline

Registered: 09/15/03
Posts: 652
Loc: boston, ma
Yup. One way or the other you need to incorporate the round trip distance.

Some equations do this by fudging the resistance values (essentially using the resistance of 2000 feet of conductor, and reporting it as the resistance for 1000 feet 'there and back again')

Others look at the voltage drop on one side only because there is assumed to be no voltage drop in the neutral.

But in all cases there needs to be some consideration of the full circuit.


#129899 - 11/09/05 04:49 PM Re: Voltage Drop Calculation
Bob Offline

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
VD=(Amps x 1 way Length x R)/1000'
This would be the correct formula if you are
using a 240 volt 2 wire circuit. There is no return distance required.
If you have a 2 wire 120 volt circuit then you need to count the return distance in the caculation.

#129900 - 11/09/05 06:03 PM Re: Voltage Drop Calculation
DiverDan Offline

Registered: 03/10/05
Posts: 38
Loc: Sacramento, CA
Also, you need to use a return distance of the square of three (1.73) for a three phase circuit.