The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
Yesterday at 09:52 PM
Safety at heights?
by gfretwell
Yesterday at 07:16 PM
failed home inspection.
by gfretwell
Yesterday at 07:03 PM
Webmaster > Admin
by Admin
Yesterday at 05:49 PM
Old Bath Fan
by gfretwell
Yesterday at 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
0 registered (), 0 Guests and 174 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129897 - 11/09/05 08:32 AM Voltage Drop Calculation
mhulbert Offline
Member

Registered: 10/19/04
Posts: 133
Loc: Anaheim, CA USA
I have an instructor telling me that to do a VD calc, you use the following formula:
VD=(Amps x 1 way Length x R)/1000'

Where R = ohm/kFt from NEC Ch 9, Table 8

It seems to me like you would have to double the length since we are only counting the resistance in one direction...is this correct? I have always used the online calculators, and I'm trying to learn how to do it on paper.

Thanks, Mike

Top
#129898 - 11/09/05 04:10 PM Re: Voltage Drop Calculation
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
Yup. One way or the other you need to incorporate the round trip distance.

Some equations do this by fudging the resistance values (essentially using the resistance of 2000 feet of conductor, and reporting it as the resistance for 1000 feet 'there and back again')

Others look at the voltage drop on one side only because there is assumed to be no voltage drop in the neutral.

But in all cases there needs to be some consideration of the full circuit.

-Jon

Top
#129899 - 11/09/05 04:49 PM Re: Voltage Drop Calculation
Bob Offline
Member

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
VD=(Amps x 1 way Length x R)/1000'
This would be the correct formula if you are
using a 240 volt 2 wire circuit. There is no return distance required.
If you have a 2 wire 120 volt circuit then you need to count the return distance in the caculation.

Top
#129900 - 11/09/05 06:03 PM Re: Voltage Drop Calculation
DiverDan Offline
Member

Registered: 03/10/05
Posts: 38
Loc: Sacramento, CA
Also, you need to use a return distance of the square of three (1.73) for a three phase circuit.
_________________________