The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by Texas_Ranger
24 minutes 10 seconds ago
100% breakers?
by Texas_Ranger
28 minutes 26 seconds ago
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 15
gfretwell 11
ghost307 10
sparkyinak 10
Trumpy 8
Who's Online
2 registered (LongRunner, Texas_Ranger), 288 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129823 - 09/09/05 10:53 AM PVC Solvent Welded Fitting Four Outside Usage ?
Robert11 Offline
Member

Registered: 08/05/05
Posts: 10
Loc: Boston, MA
Hello:

I have a project to put up an outside house flood light. Was going to use the standard 1/2 PVC electrical tubing to run the wires from where they come thru the house siding to a few feet above, where the flood light would be.
Turns, etc. would be by using the Bell junction type outside boxes.

Have a bunch of those fitting you use with PVC, and are attached "by welding" together with a Solvent.

Now I'm wondering if I'm going about this the "correct" way.

Are these Solvent Connected PVC fittings Code compliant for outside wiring where the PVC tubing and fittings would be hugging the outside house wall ?

Or, must I one liquid tight metal connectors for the PVC connections to the box ?
**(I don't know if the liquid tite connectors come in plastic also; do they ?)

Is the Code specific on this ?
Solvent PVC connection O.K. for outside
usage ?

Thanks,
Bob

Top
#129824 - 09/12/05 01:39 PM Re: PVC Solvent Welded Fitting Four Outside Usage ?
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
Solvent welding is adequate for outside use. However, I would suggest "making turns" with elbows and not with boxes.

The only reason to use a box in any conduit system is for devices or perhaps 3- or 4-way junctions with splices within.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top