The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 216 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129656 - 06/28/05 08:30 PM Shorted pilot wire in a 15KV trailing cable.
shovelelectrician Offline
Junior Member

Registered: 06/28/05
Posts: 1
Anyone familiar with trailing cable? I have a 15KV shielded cable with 3-1/0 phase conductors, 2- bare ground wires, and a #8 pilot wire. I meggered the pilot to ground 0ohms@500V Shorted. I then checked it with a circuit seeker but it showed an open circuit. So it's a insulation problem with the pilot wire. My question is: Can I use a thumper on such a small wire?(I think I know the answer to that) If not what can I do to pin point the fault? Aside from cutting the cable in halves and using the process of elimination. Any suggestions would be great. Thanks.

Top
#129657 - 08/04/05 03:46 PM Re: Shorted pilot wire in a 15KV trailing cable.
pdh Offline
Member

Registered: 01/20/05
Posts: 354
A testing device called a "time domain reflectometer" could be used to find the distance to a short. It is normally used on coaxial cable to find where cable damage is that changes the characteristic impedance. A short is a (drastic) change in impedance. This isn't the kind of thing electricians would generally have. But if you know any electrical engineers, especially those that work in RF, they may have one you could borrow.

Example products:
http://tinyurl.com/7jle5