The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 182 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129614 - 06/15/05 03:20 PM Parallel Conductors
Dnkldorf Offline

Registered: 12/12/04
Posts: 1091
Loc: nowhere usa
Some "probably stupid" questions concerning parallel conductors. Power analyzer measuring.

When measuring current on them, if you measure one set, should the other set, if the same size paralleled, be the same current draw. Ohm's law here right? Two equal paths?

When measuring KVA load, should you double the reading you see on one set, because of this? If you measure 60Kva load, it is really 120Kva load?

Power factor, should this be the same, on both sets, for instance if you measure one set and the PF was .86, that would be the total PF?

Same with Kvar and such?

Any other tid-bits you guys can throw at me, I would appreciate. I am playing around with a Fluke 434, and the manuals they give you are not real specific as to measuring paralell conductors.

(and I'm still wet behind the ears when it comes to this Power Quality stuff)



#129615 - 06/16/05 02:42 PM Re: Parallel Conductors
Radar Offline

Registered: 04/30/04
Posts: 349
Loc: Los Angeles, CA
Ohm's law counts, as does Kirchoff's (spelling?). In parallel conductors, the total load current will split between the conductors (inverse) proportional to the impedance of the conductors. If the conductors are same size & type, same length, good connections, etc, the current will split evenly. That's the goal, to have evenly loaded parallel conductors.

If the parallel cables are exactly equal, then current, kva, kvar, etc, should be the same in each.

Hope this helps some,
There are 10 types of people. Those who know binary, and those who don't.