The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 339 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129523 - 04/12/05 06:54 AM increasing primary voltage
rmiell Offline

Registered: 11/09/00
Posts: 261
Loc: La Junta, Co. USA
What effect, to the secondary voltage, will increasing the primary voltage produce? Our utility is looking to increase our distribution voltage from 13.8kV to 14.4kV (recommended by an electrical study). As long as the transformers are rated for this voltage, will the secondary voltage be increased enough to warrent looking into? We should be able to lower the taps if necessary, but will it be necessary?

Just wanted to get some basic info, as this will be engineered.


Rick Miell

#129524 - 04/12/05 10:48 AM Re: increasing primary voltage
BPiersel Offline

Registered: 01/06/05
Posts: 18
Loc: Minnesota
The secondary voltage is proportional to the primary voltage. So, for example, if the current output is 480 V, the ratio is 13800/480=28.75. At 14.4kV, the output will be 14400/28.75=500.9 V.

A simple equation you can use:

New output = (Current output/Current Primary) * New Primary

#129525 - 04/13/05 05:20 AM Re: increasing primary voltage
pauluk Offline

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
It's a 4.3% increase in voltage. I would think that you need to allow for possibility of the secondary exceeding the upper tolerance limit under low-load conditions and adjust the taps accordingly.