#129516 - 04/05/05 04:28 PM motor disconnect question
knopp Offline
Junior Member
Registered: 06/26/04
Posts: 2
Loc: richmond, va
i have two 480 3 phase motors, the first is a 10HP (14FLA)and the second is a 30HP (40FLA) these two are to be fed from individual circuit breakers at a main lug panel and a fusible disconnect supplies the incoming power. how do you properly calculate for the correct size time delay fuses at the disconnect.
Top
Tools for Electricians:
#129517 - 04/05/05 06:29 PM Re: motor disconnect question
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
How about 430.63, which would, in your case put you at 430.62?
40A x 175% = 70A
70A + 14A = 84A
84A + the lighting and appliance load on the panel = Time Delay Fuse size?

[This message has been edited by Redsy (edited 04-05-2005).]
Top