The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 327 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129516 - 04/05/05 04:28 PM motor disconnect question
knopp Offline
Junior Member

Registered: 06/26/04
Posts: 2
Loc: richmond, va
i have two 480 3 phase motors, the first is a 10HP (14FLA)and the second is a 30HP (40FLA) these two are to be fed from individual circuit breakers at a main lug panel and a fusible disconnect supplies the incoming power. how do you properly calculate for the correct size time delay fuses at the disconnect.

#129517 - 04/05/05 06:29 PM Re: motor disconnect question
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
How about 430.63, which would, in your case put you at 430.62?
40A x 175% = 70A
70A + 14A = 84A
84A + the lighting and appliance load on the panel = Time Delay Fuse size?

[This message has been edited by Redsy (edited 04-05-2005).]