#129422 - 03/04/05 08:31 AM Article 250.4 (B)(2)
unsaint32 Offline
Member
Registered: 08/24/04
Posts: 16
Loc: eden prairie, MN, USA
A quote from 250.4 (B)UNGROUNDED SYSTEM (2) , "[equipment bonding] shall be connected together and to the supply system grounded equipment."

Does the "supply system grounded equipment" indicate that the supply system is system-grounded? Or does that just mean that the suuply system's equipment bonding is connected to earth? (because an ungrounded system's equipment bonding gets connected to earth, but not to the power source)
Top
Tools for Electricians:
#129423 - 03/18/05 11:35 AM Re: Article 250.4 (B)(2)
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 826
Loc: Michigan
Means Equipment grounding(bonding) conductors well tie together to reference ground.An ungrounded system must be grounded the same as a grounded system even thought theres no reference from phase conductors to ground. Reason if one phase goes to ground(ground dector lights) nothing but an alarm or Ground dection light going out. BUT if one phase goes out then another the bonding conductors Must be able to carry fault.Why are theses systems used. Water treament plants, sewage plants areas where going dn at the ist fault is not a option. Gives the operator time when ist fault is noticed to schedule a shutdn and take care of the problem.Thats the way I see it. I;ve worked on several of theses systems as our power company well no longer supply a high leg delta but well supply an ungrounded or one leg grounded system.For better info see Electrical Grounding 6th edition (Ronald P.O;Riley page (90) or Soares grounding book
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
License exam
by TRUE POWER
Today at 09:16 PM
Looking for older post
by sparkyinak
Today at 12:27 AM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 74 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 03/13/07
Posts: 167

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals