The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Search Function
by Webmaster
01/18/17 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
01/18/17 09:17 PM
ESA Arc flash course
by frank
01/18/17 04:25 PM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 29
HotLine1 21
Ruben Rocha 16
Trumpy 12
ghost307 12
Who's Online
1 registered (Webmaster), 0 Guests and 183 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129393 - 02/17/05 09:42 AM information
engelectric@aol.com Offline
Junior Member

Registered: 02/19/03
Posts: 1
Loc: marshfield
have a 30 kva transformer feeding a 100 amp 208/120 need to add 70 more amp to load.the phases are reading A-9.2 B-1.7 C-1.6 the 30 amp breaker feeding the transformer is from a 480/277 panel.that main breaker is a 50 amp being feed from the outside 100 amp fuse disconnect. will i have to chage any breaker size.from the main fuses to the 480/277 panel and to the 208/120 panel.

Top
#129394 - 02/17/05 03:41 PM Re: information
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
What type and size conductors on the secondary???

Do you have a 30 and a 50amp pri OCP??

Look at 450.3(B) and the table
240.6.

kVA = V.A / 1000 Single phase
kVA = V.A.1.73 / 1000 Three Phase

or read the charts

Charlie

Top