The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (Tjia1981), 85 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129393 - 02/17/05 09:42 AM information Offline
Junior Member

Registered: 02/19/03
Posts: 1
Loc: marshfield
have a 30 kva transformer feeding a 100 amp 208/120 need to add 70 more amp to load.the phases are reading A-9.2 B-1.7 C-1.6 the 30 amp breaker feeding the transformer is from a 480/277 panel.that main breaker is a 50 amp being feed from the outside 100 amp fuse disconnect. will i have to chage any breaker size.from the main fuses to the 480/277 panel and to the 208/120 panel.

#129394 - 02/17/05 03:41 PM Re: information
cpal Offline

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
What type and size conductors on the secondary???

Do you have a 30 and a 50amp pri OCP??

Look at 450.3(B) and the table

kVA = V.A / 1000 Single phase
kVA = V.A.1.73 / 1000 Three Phase

or read the charts