The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
0 registered (), 74 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129346 - 01/25/05 02:49 PM 3 phase current calculations
DJT Offline
Junior Member

Registered: 01/25/05
Posts: 2
Loc: Indianapolis, In. 46221
I AM PROVIDING TRAINING FOR OUR PLANT ELECTRICIANS, AND I WANT TO CONFIRM A COUPLE BITS OF POWER THEORY PRIOR TO GOING LIVE.

EXAMPLE: 13,800V DELTA, 480-277V WYE, 2000KVA
TRANSFORMER.
X1 HAS 1000 AMPS
X2 HAS 1200 AMPS
X3 HAS 1400 AMPS

I HAVE ASKED THEM TO CALCULATE:
NEUTRAL CURRENT
ALL 3 DELTA LINE CURRENTS
ALL 3 DELTA PHASE CURRENTS

TO SOLVE FOR NEUTRAL CURRENT;
THE SQUARE ROOT OF...
1000 SQUARED + 1200 SQUARED + 1400 SQUARED
= 2098 AMPS
DELTA PHASE A CURRENT = 1000A/49.819 = 20AMPS
............B CURRENT = 1200A/49.819 = 24AMPS
............C CURRENT = 1400A/49.819 = 28AMPS
49.819 IS 13800/277.
DELTA A LINE CURRENT = 20 X 1.732 = 35AMP
......B LINE CURRENT = 24 X 1.732 = 42AMP
......C LINE CURRENT = 28 X 1.732 = 48AMP

I REALIZE THAT WITH THESE IMBALANCES, THERE WILL BE PHASE SHIFTS, BUT 120 DEGREE ANGLES WERE USED TO SIMPLIFY.
I HAVE A 50/50 CONFIDENCE LEVEL WITH MY CALCULATIONS.

Top
#129347 - 01/25/05 04:28 PM Re: 3 phase current calculations
crash Offline
Member

Registered: 10/21/03
Posts: 130
Loc: Calgary Canada
I got 346.4A for the neutral current. The other figures seem to be correct.

The neutral current is calculated by adding the line currents in a vectoral manor.

[This message has been edited by crash (edited 01-25-2005).]

Top
#129348 - 01/25/05 06:34 PM Re: 3 phase current calculations
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
The Delta line currents are the vector sum of the phase currents at each node, so you can't simply multiply the phase currents by root three. Even if you are making the simplifying assumption of 120 degrees between each phase, I get 38.16A, 41.62A, 45.08A...I've not double checked this.

-Jon

Top
#129349 - 01/26/05 05:21 AM Re: 3 phase current calculations
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
Try this it' always worked for me.

I N =Sq root of A2 + B2 + C2 – A.B-B.C-C.A

Essentially this provides the vector sum of the three currents. It works if one phase is not utilized also.

Top
#129350 - 01/28/05 04:39 PM Re: 3 phase current calculations
scameron81 Offline
Member

Registered: 02/24/04
Posts: 80
Loc: Healdsburg, ca, USA
Here is a great explanation of the nuetral currents on wye systems. It even has the formula to calculate the netrual current.
http://www.electrician.com/electa1/electa3htm.htm