ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
Anyone hiring inspectors?
by HotLine1. 03/27/17 08:03 AM
Old decora style outlets
by Admin. 03/25/17 11:40 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,576 Are you busy
166,374 Re: Forum
160,686 Need opinion
Who's Online Now
2 registered members (geoff in UK, HotLine1), 72 guests, and 13 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#129332 - 01/21/05 09:50 PM open delta banking concerns  
splitzapper  Offline
Junior Member
Joined: Jan 2005
Posts: 6
Davao
hello there..friends please help me with my problem.
Is it possible to bank 2 transformers in open delta if it has different kva rating?
assuming that both have the same voltage rating,impedance ratio and frequency.
If it is possible, then how would i compute the power contribution of each transformer?
your inputs would truly be appreciated.
thanks in advance,.,.


Oh Yeah!

Tools for Electricians:

#129333 - 01/22/05 12:01 AM Re: open delta banking concerns  
peterpang  Offline
Member
Joined: Jan 2005
Posts: 19
toronto
My answer to your question is yes!
As I know there are 7 condictions should be met when you parallel 2 transformers:

1)P-S voltage must be the same!
2)Proper polarities connetion
3)Percentage impedence of one is between 92.5% and 107.5% of the other
4)Same tap setting
5)Identical phase displacements.
6)Identical frequency
7)Equivalent impedence and X/R ratio

So I think it is possible to bank 2 transformers in open delta even if they have different kva ratings!!!
And the total Apparent Power=(P1+P2)x86.6%!


#129334 - 01/22/05 12:30 AM Re: open delta banking concerns  
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA
The utilities do this all the time. You might have a 50 kva and a 10 kva banked together. This is done when the 3 phase load is small. The 3 phase load is 57% on each transformer and the lighting transformer(50kva) will carry 100% of the single phase load.

[This message has been edited by Bob (edited 01-21-2005).]


#129335 - 01/22/05 02:09 AM Re: open delta banking concerns  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
 
There are some assorted cut-and-paste notes from El Paso Electric on non-symmetrical delta- and open-delta-secondary transformer banks. [It is unnecessary that the pair of transformers be matched.] These configurations are mostly intentionally unsymmetrical to allow for inherently unbalanced 1ø and 3ø loads.

Save file http://6L6.net/bjarn/ecn.DSOexcerpt-7delta.pdf ~1.1MB {available for a short time}

Another [fee-based] reference is §8 in ANSI/IEEE Std C57.105-1978 …Application of Transformer Connections in Three-Phase Distribution Systems.




[This message has been edited by Bjarney (edited 01-22-2005).]


#129336 - 01/22/05 03:10 AM Re: open delta banking concerns  
splitzapper  Offline
Junior Member
Joined: Jan 2005
Posts: 6
Davao
guys thanks a lot. now it is clearer to me.i hope you would still answer mr questions cause i have a lot. btw i am a newly licensed practitioner so your inputs would truly help me...once again thanks..


Oh Yeah!

#129337 - 03/06/05 12:40 PM Re: open delta banking concerns  
marcel1444  Offline
Junior Member
Joined: Mar 2005
Posts: 1
so.windsor ct usa
The seven requirements are important when paralleling transformers.This is when the transformers primarys are connected together and their secondaries feed the same load. When you are banking transformers
like three transformers feeding a three phase load or two transformers in an open delta configuration the impeedance is not important. The only exception is primary delta and secondary delta. Then you want to have your impeedances close. In the case of the open delta with the 50kva and the 10 kva you woutd be just fine. If you bank a transformer with two others the one with the lower impedance will take more of the load. Being that the impedance of the 50kva is most likely lower than the 10 kva you are in good shape.


marcel1444


Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.022s Queries: 14 (0.005s) Memory: 0.7748 MB (Peak: 0.9222 MB) Zlib enabled. Server Time: 2017-03-27 18:27:14 UTC