The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm² flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 276 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129332 - 01/21/05 05:50 PM open delta banking concerns
splitzapper Offline
Junior Member

Registered: 01/21/05
Posts: 6
Loc: Davao
hello there..friends please help me with my problem.
Is it possible to bank 2 transformers in open delta if it has different kva rating?
assuming that both have the same voltage rating,impedance ratio and frequency.
If it is possible, then how would i compute the power contribution of each transformer?
your inputs would truly be appreciated.
thanks in advance,.,.
Oh Yeah!

#129333 - 01/21/05 08:01 PM Re: open delta banking concerns
peterpang Offline

Registered: 01/08/05
Posts: 19
Loc: toronto
My answer to your question is yes!
As I know there are 7 condictions should be met when you parallel 2 transformers:

1)P-S voltage must be the same!
2)Proper polarities connetion
3)Percentage impedence of one is between 92.5% and 107.5% of the other
4)Same tap setting
5)Identical phase displacements.
6)Identical frequency
7)Equivalent impedence and X/R ratio

So I think it is possible to bank 2 transformers in open delta even if they have different kva ratings!!!
And the total Apparent Power=(P1+P2)x86.6%!

#129334 - 01/21/05 08:30 PM Re: open delta banking concerns
Bob Offline

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
The utilities do this all the time. You might have a 50 kva and a 10 kva banked together. This is done when the 3 phase load is small. The 3 phase load is 57% on each transformer and the lighting transformer(50kva) will carry 100% of the single phase load.

[This message has been edited by Bob (edited 01-21-2005).]

#129335 - 01/21/05 10:09 PM Re: open delta banking concerns
Bjarney Offline

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
There are some assorted cut-and-paste notes from El Paso Electric on non-symmetrical delta- and open-delta-secondary transformer banks. [It is unnecessary that the pair of transformers be matched.] These configurations are mostly intentionally unsymmetrical to allow for inherently unbalanced 1ø and 3ø loads.

Save file ~1.1MB {available for a short time}

Another [fee-based] reference is §8 in ANSI/IEEE Std C57.105-1978 …Application of Transformer Connections in Three-Phase Distribution Systems.

[This message has been edited by Bjarney (edited 01-22-2005).]

#129336 - 01/21/05 11:10 PM Re: open delta banking concerns
splitzapper Offline
Junior Member

Registered: 01/21/05
Posts: 6
Loc: Davao
guys thanks a lot. now it is clearer to me.i hope you would still answer mr questions cause i have a lot. btw i am a newly licensed practitioner so your inputs would truly help me...once again thanks..
Oh Yeah!

#129337 - 03/06/05 08:40 AM Re: open delta banking concerns
marcel1444 Offline
Junior Member

Registered: 03/03/05
Posts: 1
Loc: so.windsor ct usa
The seven requirements are important when paralleling transformers.This is when the transformers primarys are connected together and their secondaries feed the same load. When you are banking transformers
like three transformers feeding a three phase load or two transformers in an open delta configuration the impeedance is not important. The only exception is primary delta and secondary delta. Then you want to have your impeedances close. In the case of the open delta with the 50kva and the 10 kva you woutd be just fine. If you bank a transformer with two others the one with the lower impedance will take more of the load. Being that the impedance of the 50kva is most likely lower than the 10 kva you are in good shape.