The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 299 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129284 - 01/03/05 07:33 AM single phase from three phase
randyagr Offline
Junior Member

Registered: 03/07/04
Posts: 6
Loc: Lanark, IL US
Let's say I have a v-phase primary (2 hots plus a nuetral) with a 3 phase center tap open delta service drop(3 hots plus a nuetral) Each phase is 120 degrees apart, but if I take 2 leads for a sigle phase application, the phases are 180 degrees apart. How does this happen? Also, how many degrees apart are the phases on the primary? Thanks. Randy.

#129285 - 01/03/05 07:37 PM Re: single phase from three phase
winnie Offline

Registered: 09/15/03
Posts: 652
Loc: boston, ma
I just about wrote an essay related to this topic last week:

You cannot define phase angle with a single circuit. You only get a phase angle measurement when you have _two_ or more circuits, and can describe the phase angle difference between them.

If you supply a single phase line to line load from a three phase source, than as far as that load is concerned, there is no phase angle. You only have two terminals, with first one then the other alternatively being relatively positive.

Once you have two circuits defined, _then_ you can find a phase angle difference. With your 'V' primary, you have three circuits; neutral to A, neutral to B, and A to B. If we _define_ the phase of the neutral to A circuit as zero degrees, then the neutral to B circuit is 120 degrees. I believe that the A to B circuit has a phase angle of 150 degrees with an amplitude of 1.732 * the amplitude of the neutral to A circuit, but I'm not going to swear to that without doing the math out on paper.


#129286 - 01/03/05 08:25 PM Re: single phase from three phase
Bjarney Offline

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
For an open-delta secondary, there are two possible configurations for the primary side of the transformer bank. One is open-wye, with 120° between two phase-to-neutral primary connections. The other is open-delta, with 60° between two phase-to-phase-connected primary windings, that are typically symmetrical with the two secondary windings.

[This message has been edited by Bjarney (edited 01-04-2005).]