#129265 - 12/19/04 08:37 AM 12 Lead Stator Gennys Discussion  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
12 Lead Stator Gennys Discussion

Feel free to discuss the newly posted 12 Lead Stator Generator Schematics, created for ECN by Bjarney.

These items are located in the Technical Reference Area, under the Topic:

12 Lead Stator Generators Schematics

Click the link above to view the Schematics page.

I will get the ball rolling [Linked Image]

Bjarney,

Could you please elaborate a bit on these items - especially the Delta Connection, which is labeled as "Derated" and "120/240 VAC 1Ø 3W?

Thanks for the contributions!

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Tools for Electricians:

#129266 - 12/19/04 09:25 PM Re: 12 Lead Stator Gennys Discussion  
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
That 120/240 Single Phase connection has my curiosity.


#129267 - 12/20/04 02:12 PM Re: 12 Lead Stator Gennys Discussion  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
 
Derating to 2/3 for Edison 1ø 3-wire service on a 12-lead generator comes from not using the efficiency of three phase for loading. Else, a nameplated-30kW/37½kVA genset can only support a 20kW/25kVA load in 1ø 3w service.

Example — Each of six coils in a 30kW stator is rated 5kW. On the 1ø 3w application, referring to the 1ø interconnection schematic, the stator has two sets of three 120-volt windings in a pair of delta groups. For ½ of the windings, T1-T4 coil has a rating of 5kW of load, as do coils T2-T5 and T3-T6. BUT, the interconnected T2-T5/T3-T6 provides 5kW of capacity in phase with T1-T4 coil, for a total of 10kW at 120V. In this case, two 120V 5kW coils can only provide 5kW (not 10) of generator capacity. {Cosine 60° = 0.5} The same holds true for the other half with T8-T11/T9-T12 pair in parallel with T7-T10, providing 5 + 5 or 10kW for each group of three delta-connected coils, with a grand total of 10 + 10 = 20kW for 120/240V 3-wire output.




[This message has been edited by Bjarney (edited 12-20-2004).]


#129268 - 12/21/04 08:41 PM Re: 12 Lead Stator Gennys Discussion  
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
Whould the single phase connection work on a 12 Lead 3Phase motor?


#129269 - 12/21/04 11:31 PM Re: 12 Lead Stator Gennys Discussion  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
 
Reasonably certain it would not.



Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,137
Joined: May 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7670 MB (Peak: 0.9040 MB) Zlib enabled. Server Time: 2017-03-30 20:24:36 UTC