#129220 - 11/01/04 10:44 PM Unbalanced delta calculations
u2slow Offline
Member
Registered: 09/18/03
Posts: 198
Loc: Salt Spring, BC, Canada
I'm in 3rd year school right now, and some of the 3-phase math is getting me down... unbalanced delta loads specifically - trying to figure out the line currents.

Our instructor's method works but the values he chooses and when he uses them seems arbitrary. Put the wrong two phasors head to tail, and the resultant in meaningless.

Anyone have some tips or tricks?
Top
Tools for Electricians:
#129221 - 11/06/04 06:14 PM Re: Unbalanced delta calculations
crash Offline
Member
Registered: 10/21/03
Posts: 130
Loc: Calgary Canada
There are no "Tricks" in 3 phase, phasor calculations. Just math.

Can You post a specific problem with (or with-out) your instructors solution? And also what your instructor choose in an "arbitrary" manor?
Top
#129222 - 11/06/04 08:01 PM Re: Unbalanced delta calculations
u2slow Offline
Member
Registered: 09/18/03
Posts: 198
Loc: Salt Spring, BC, Canada
I figured it out (Thanks for responding!)

My instructor was busy disecting each phasor into X and Y values with sin/cos functions and subtracting them. It just didn't make sense until he showed what he was doing with a phasor diagram and finally had a 3-blade propellor drawn on the board. *Now* that made a whole lot more sense! I worked through a few more problems with the diagrams only... and solved them all. Now the original purely-arithmetic method is starting to make sense. Go figure

What I found arbitrary was how he assigned the A, B, & C phase subscripts to the current phasors. I now know it doesn't matter - you get same answers no matter how you do it.

Here is one of the problems. I'll see if I can transcribe the solution and post it up.

Q:

The phase currents in a delta-connected, unbalanced load are 20A, 32A, and 40A. Calculate the three line currents, if all loads are resistors.

A:

52.92A, 62.35A, 45.43A
Top
#129223 - 11/07/04 10:13 PM Re: Unbalanced delta calculations
crash Offline
Member
Registered: 10/21/03
Posts: 130
Loc: Calgary Canada
I got the same answers as you on that problem. It took a little while for me to remember how to do it though.
Top
#129224 - 11/09/04 07:50 PM Re: Unbalanced delta calculations
Peter Offline
Member
Registered: 06/08/04
Posts: 93
Loc: San Diego
I am confused here. What is the equation? I thought it would be amps times the square root of three.
~Peter
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 110 Guests and 17 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals