#129152 - 08/19/04 08:28 AM Shaded Pole Motor Control
TimK Offline
Junior Member
Registered: 08/19/04
Posts: 2
Loc: Witney, Oxfordshire,UK
I need to speed control a 2 pole, shaded pole motor that runs a fan. I have used a simple triac 'light dimmer' control but the harmonic content at low speed settings means there is much vibration in the motor. Any ideas? Is there a simple PWM controller I could use?
Top
Tools for Electricians:
#129153 - 08/23/04 02:27 AM Re: Shaded Pole Motor Control
Frank Martino Offline
New Member
Registered: 05/04/04
Posts: 7
Loc: Middlebury, CT, USA
Airmaster Fan sells a control manufactured by KB Electronics. It is rated for use with motors.

I assume the difference between the light dimmer and the motor rated unit is added inductance to attenuate the inrush current. The units are cheap enouph to make it worth a try.
Top
#129154 - 08/23/04 03:05 AM Re: Shaded Pole Motor Control
TimK Offline
Junior Member
Registered: 08/19/04
Posts: 2
Loc: Witney, Oxfordshire,UK
Many Thanks, I will try them and let you know how I get on.
Top
#129155 - 10/27/04 01:18 PM Re: Shaded Pole Motor Control
arm Offline
Junior Member
Registered: 10/27/04
Posts: 1
Loc: Manchester, NH, USA
what's the difference between a shaded pole motor and a brush type motor ?

[edit: found the answer online elswhere]:
http://www.all-science-fair-projects.com...nchronous_motor


[This message has been edited by arm (edited 10-27-2004).]
Top
#129156 - 10/27/04 02:09 PM Re: Shaded Pole Motor Control
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Quote:

what's the difference between a shaded pole motor and a brush type motor ?


A Shaded Pole Motor is a Brushless type, Single Phase Squirrel Cage Induction Motor, with a Short Circuited "Secondary" (Rotor), and a Shading Pole in the "Primary" (Stator) for Starting.

A Brush type Motor has Brushes contacting a Commutator, which is mounted on a rotatable, wound Armature.
The Commutator segments feed to/from the Windings on the Armature assembly.

There are a few AC Induction Motors with Commutators & Brushes (Syncronous, Repulsion Start, etc.), but for the most part, Induction Motors are Brushless Animals, with the Stator (Primary) Windings Physically Isolated (not connected in a "Physical" way), from the Rotor (Secondary).

The Stator would kind of equate to the Field windings of a Commutator Motor, and the Rotor equates to the Armature of a Commutator Motor.

They work nothing like one another - one functions via Induction, the other Repulsion.

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 57 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals