The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 102 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129091 - 07/12/04 07:26 AM 5VDC TO 4-20mA Conversion
rad74ss Offline
Member

Registered: 04/19/04
Posts: 154
Loc: Pryor, OK USA
I need help trying to figure out how to convert a 0-5vdc signal to 4-20mA. This is to convert the signal on a 0-500psi transducer.

The company wants to use resistors instead of buying a converter.

I would appreciate any help from the electronically inclined electricians.

Thanks.

Robert

Top
#129092 - 07/12/04 08:57 AM Re: 5VDC TO 4-20mA Conversion
mistermike Offline
Junior Member

Registered: 05/17/04
Posts: 3
Without going into a long-winded dissertation, forget about using resistors. The differences in the "zero" point base (0 volts vs. 4 mA) and in how instrument designs handle voltages versus currents do not lend themselves to a simple conversion using only resistors.

A 0-5V/4-20mA signal conditioner can be bought for around $250. You will burn up that money in a heartbeat trying to configure and calibrate a homebrew resistor setup.

Top
#129093 - 07/12/04 09:54 AM Re: 5VDC TO 4-20mA Conversion
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
5V/0.020A=250Ω, but it’s not usually that simple.

There is an offset problem for transducer output—below 1 volt, the current channel will treat the reading as zero, or as a signal error when under 4mA. A resistor may work with the right 4-20mA transducer output and 1-5V input channel.

Top
#129094 - 07/10/05 06:10 PM Re: 5VDC TO 4-20mA Conversion
NJwirenut Offline
Member

Registered: 09/15/01
Posts: 816
Loc: Bergen County, NJ
If you are handy with a soldering iron, you could build your own V/I converter using a chip like the XTR110 from Burr-Brown:
http://kolter.de/xtr110.pdf

Because you need to source 4 mA of current with zero voltage input, you will NEVER get ther with a purely passive network of resistors.

Top
#129095 - 07/12/05 09:36 AM Re: 5VDC TO 4-20mA Conversion
IanR Offline
Member

Registered: 12/06/04
Posts: 326
Loc: Palm Bay FL USA
if you're can read a schematic and use a soldering iron try here: http://www.discovercircuits.com/C/co-vtoc.htm

also a good source for many other circuits

Top
#129096 - 07/12/05 10:19 AM Re: 5VDC TO 4-20mA Conversion
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Robert,
Are you sure that you need a conveter? Many 4-20ma inputs just use a 250 ohm resistot internal to convert the current to a voltage, and many have a setting that will change the input from 4-20 to 0-20. If both of these conditions are present, all you have to do is to remove the internal resistor and change the setting to 0-20ma.
Don