The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 08:52 AM
Would ELV branch circuits be a good idea?
by geoff in UK
Today at 03:25 AM
Why cables look like they do
by Trumpy
Today at 02:20 AM
Re: Fabricating Guards out of Lexan?
by Trumpy
Today at 12:36 AM
100% breakers?
by Texas_Ranger
Yesterday at 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 16
Trumpy 12
Webmaster 12
ghost307 10
frank 9
Who's Online
1 registered (ghost307), 0 Guests and 73 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129058 - 07/08/04 03:59 AM Generator load hunting problem
luckyali Offline
Junior Member

Registered: 06/22/04
Posts: 7
Loc: pakistan
Three generators (1000KVA,800Kw,415V)are running in parallel almost on 500Kw each,but generator A is variating form 50 to 1500Kw when it runn on 400Kw (this was measured on recorder,it measures the both min & max vales) while the actuator voltages are constatnt.Please tell me the cause of load hunting.

Top
#129059 - 07/08/04 04:03 AM Re: Generator load hunting problem
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
When 'A' is hunting, are the other two gens compensating by picking up excess load?
How are you accounting for load sharing among the three gens?
_________________________
Ron

Top
#129060 - 07/08/04 06:47 AM Re: Generator load hunting problem
luckyali Offline
Junior Member

Registered: 06/22/04
Posts: 7
Loc: pakistan
No,two other generator pick up load only when speed drops of any one,there is no variation in speed,i already told that actuator voltage of A are constant.load sharing is controlled by 2301A woodward speed sharing and load control unit.

[This message has been edited by luckyali (edited 07-08-2004).]

Top
#129061 - 07/08/04 11:47 AM Re: Generator load hunting problem
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
If you have studied the Woodward instruction book and not resolved the problem, you might contact their technical-support group. From a distance, it is hard to tell whether it is a configuration problem or one internal to the Woodward components.

Top
#129062 - 07/10/04 02:41 PM Re: Generator load hunting problem
uksparky Offline
Member

Registered: 07/06/04
Posts: 199
Loc: UK
Sounds to me like a synchronising issue - definitely a sharing/control matter. Speed variation in gennys? Hmm. If a diesel set hunts its generally an injection pump governor problem, or the same for petrol but on the carb. However, this would result in cyclic problems and a host of other evils - and dropping like flies of breakers.

Several years ago I got up one morning to find the lights fluctuating from about 50% to full on roughly 2.5cps. The tv didn't like it at all!! This lasted about ten minutes before we had a 30 second outage then back to normal. A few days later I saw our chief utility troubleshooter in the village and asked him what it was about. His reply was that it was something that theoretically couldn't happen; the ( at that time ) two alternators supplying our region ( we were disconned from the national grid for repairs over the weekend ) had got out of sync with each other; the control system had crashed. I never stopped to work it out, but I guess it is theoretically possible, especially if balancing/motive force is not up to scratch.

Call up the load-box suppliers
_________________________
If hindsight were foresight, we'd all be millionaires!

Top


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals