Why do you think the code prohibits running parallel conductors smaller than 1/0??
Top
Tools for Electricians:
#128975 - 06/09/04 09:00 AM Re: Parallel conductors
Creighton Offline
Member
Registered: 01/06/02
Posts: 59
Loc: Hayward, CA
If you study the ampacity tables you will see that in the larger sizes of wire an increase in size results in relatively little increase in ampacity. Forinstance, a 50% increase from 10 kcmil to 10.5 kcmil results in an increase in carrying capacity in amperes of less than 15%.
There is no need to parallel conductors smaller than 1/0 because the difference between the carrying capacity in these sizes is much less pronounced.
Although the NEC places the limit, it is really physics that limits paralleled conductors to 1/0 and larger.
Creighton
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 35 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals