The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 81 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#128974 - 06/09/04 06:37 AM Parallel conductors
ayrton Offline

Registered: 12/21/01
Posts: 205
Loc: Pa
Why do you think the code prohibits running parallel conductors smaller than 1/0??

#128975 - 06/09/04 09:00 AM Re: Parallel conductors
Creighton Offline

Registered: 01/06/02
Posts: 56
Loc: Hayward, CA
If you study the ampacity tables you will see that in the larger sizes of wire an increase in size results in relatively little increase in ampacity. Forinstance, a 50% increase from 10 kcmil to 10.5 kcmil results in an increase in carrying capacity in amperes of less than 15%.
There is no need to parallel conductors smaller than 1/0 because the difference between the carrying capacity in these sizes is much less pronounced.
Although the NEC places the limit, it is really physics that limits paralleled conductors to 1/0 and larger.